The BNI EIP-508-105-Z015 is an IO-LINK master (If I use the terminology correct, remember newbie here)

It is on the network and you can grab sensor data by going to address/ports.jsn

IO-LINK seems to be a popular standard… but looking around would it normally connect to a PLC before being connected to say ignition ?

Or would a different master be the way to go? This looks pretty straight forward [https://comtrol.com/wp-content/uploads/Ignition-via-OPC-UA.pdf](https://comtrol.com/wp-content/uploads/Ignition-via-OPC-UA.pdf)

---

<div class="post-metadata">

**Author:** ![chi](https://avatars.discourse-cdn.com/v4/letter/c/0ea827/32.png) [@chi](https://forum.inductiveautomation.com/u/chi)\
**Post date:** [September 18, 2019, 7:04pm UTC](https://forum.inductiveautomation.com/t/complete-newbie-how-to-add-a-bni-eip-508-105-z015/28360/2 "2019-09-18T19:04:47Z")

</div>

The Balluff EIP Modules are Ethernet/IP modules. Normally they are used as remote IO for a master plc.  
Your module supports I/O link sensors in addition to the standard binary IO ports, but the network protocol is still Ethernet/IP.  
Maybe @pturmel can tell you if his Ethernet/IP module [http://forum.inductiveautomation.com/t/snappy-user-interfaces-with-the-ethernet-ip-module/12617](http://forum.inductiveautomation.com/t/snappy-user-interfaces-with-the-ethernet-ip-module/12617) will work with your device.

---

<div class="post-metadata">

**Author:** ![mellerbeck](https://avatars.discourse-cdn.com/v4/letter/m/e9bcb4/32.png) [@mellerbeck](https://forum.inductiveautomation.com/u/mellerbeck)\
**Post date:** [September 18, 2019, 8:10pm UTC](https://forum.inductiveautomation.com/t/complete-newbie-how-to-add-a-bni-eip-508-105-z015/28360/3 "2019-09-18T20:10:49Z")

</div>

So you would normally point ignition at say the Allen Bradley PLC that was connected to the sensors through I/O link.

This gear is new, so if something else should be bought or configured differently I would try and go that route.

---

<div class="post-metadata">

**Author:** ![chi](https://avatars.discourse-cdn.com/v4/letter/c/0ea827/32.png) [@chi](https://forum.inductiveautomation.com/u/chi)\
**Post date:** [September 18, 2019, 8:27pm UTC](https://forum.inductiveautomation.com/t/complete-newbie-how-to-add-a-bni-eip-508-105-z015/28360/4 "2019-09-18T20:27:57Z")

</div>

> [@mellerbeck](#):
>
> So you would normally point ignition at say the Allen Bradley PLC that was connected to the sensors through I/O link.

Almost. The plc is connected through Ethernet/IP.

If you need to connect I/O link sensors direct to Ignition, an OPC-UA gateway might be a simplier solution. [https://comtrol.com/io-link-master-gateways-infographic](https://comtrol.com/io-link-master-gateways-infographic)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [September 19, 2019, 5:46am UTC](https://forum.inductiveautomation.com/t/complete-newbie-how-to-add-a-bni-eip-508-105-z015/28360/5 "2019-09-19T05:46:29Z")

</div>

> [@chi](#):
>
> Maybe @pturmel can tell you if his Ethernet/IP module [http://forum.inductiveautomation.com/t/snappy-user-interfaces-with-the-ethernet-ip-module/12617](http://forum.inductiveautomation.com/t/snappy-user-interfaces-with-the-ethernet-ip-module/12617) will work with your device.

I would expect it to, in scanner mode (premium version). I'd need to inspect the EDS file to confirm.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [January 16, 2020, 10:19pm UTC](https://forum.inductiveautomation.com/t/complete-newbie-how-to-add-a-bni-eip-508-105-z015/28360/6 "2020-01-16T22:19:03Z")

</div>

Follow-up:

This device has been reported to work with [this XML configuration](https://www.automation-pros.com/enip1/Balluff-BNI006A.xml). Note that the **BNI EIP-508-105-Z015** is also known as the **BNI006A**.

The config can be cut down a bit to work with the similar BNI004A. It supports IOLink on four of its eight ports, instead of all eight.