I need to create an Ignition application that logs 4 analog points. Is there a way to connect to IO directly without using a PLC?  
Data points will be 4-20ma or PT100 RTDs

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [June 9, 2015, 2:19am UTC](https://forum.inductiveautomation.com/t/connect-directly-to-io/10108/2 "2015-06-09T02:19:29Z")

</div>

I haven’t used the ADAM series in a long time, but its Modbus TCP support should work for you. Model [ADAM-6017](https://gridconnect.com/8-channel-analog-input-w-do-ethernet-module-adam-6017.html) or one of its siblings look right.

---

<div class="post-metadata">

**Author:** ![EricFrancoeur](https://avatars.discourse-cdn.com/v4/letter/e/dfb087/32.png) [@EricFrancoeur](https://forum.inductiveautomation.com/u/EricFrancoeur)\
**Post date:** [June 10, 2015, 2:28pm UTC](https://forum.inductiveautomation.com/t/connect-directly-to-io/10108/3 "2015-06-10T14:28:48Z")

</div>

We’ve used ADAM 6015 as modbus TCP (Probably the similar setting)

The weird thing with those is to get the Values, you have to create the tag manually as I can recall and the OPC Item Path looks like [Adam 6015 Burner 1]HR1, [Adam 6015 Burner 1]HR2 and so forth.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [June 10, 2015, 3:08pm UTC](https://forum.inductiveautomation.com/t/connect-directly-to-io/10108/4 "2015-06-10T15:08:10Z")

</div>

[quote=“EricFrancoeur”]We’ve used ADAM 6015 as modbus TCP (Probably the similar setting)

The weird thing with those is to get the Values, you have to create the tag manually as I can recall and the OPC Item Path looks like [Adam 6015 Burner 1]HR1, [Adam 6015 Burner 1]HR2 and so forth.[/quote]

You’ll have to create the tag manually for any Modbus device. Modbus is a very simple protocol with no notion of browsing or discovery.

---

<div class="post-metadata">

**Author:** ![Curlyandshemp](https://avatars.discourse-cdn.com/v4/letter/c/bcef8e/32.png) [@Curlyandshemp](https://forum.inductiveautomation.com/u/Curlyandshemp)\
**Post date:** [June 19, 2015, 10:09pm UTC](https://forum.inductiveautomation.com/t/connect-directly-to-io/10108/5 "2015-06-19T22:09:08Z")

</div>

[quote=“Kevin.Herron”][quote=“EricFrancoeur”]We’ve used ADAM 6015 as modbus TCP (Probably the similar setting)

The weird thing with those is to get the Values, you have to create the tag manually as I can recall and the OPC Item Path looks like [Adam 6015 Burner 1]HR1, [Adam 6015 Burner 1]HR2 and so forth.[/quote]

You’ll have to create the tag manually for any Modbus device. Modbus is a very simple protocol with no notion of browsing or discovery.[/quote]

Just received the Adam. Very easy to setup and configure.  
Manually created Modbus tags reading the HR registers and it work! Connected RTD to 4-20ma transmitter as input to Adam.