Hi,

I’am using Ignition to monitor remote sites.For one of this site, I have an ABB OPC DA server installed, which I’d like to connect to my main Ignition gateway thanks to the OpcCom Tunneller module.

Ignition UA server and OpcCom Tunneller have been successfully installed on the remote machine and work fine.

My problem is I can’t get the main Ignition gateway to connect to the remote Ignition UA server. I tried on the same machine as the main gateway with the OPC Unified Automation client and it works perfectly …

I don’t understand what I’am missing with the server connection configuration.  
Here are the error messages I get from the console:

Quote:  
Error connecting to server: StatusCode[Severity=Bad, Subcode=Bad\_ConnectionRejected]

I guess it should be either a certificate or a endpoints adress problem.

Thanks for your support.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [July 31, 2014, 12:50pm UTC](https://forum.inductiveautomation.com/t/connect-ignition-ua-server-to-a-second-ignition-ua-server/8828/2 "2014-07-31T12:50:59Z")

</div>

Is the endpoint address on the remote server set up correctly? (UA Settings on the remote)

---

<div class="post-metadata">

**Author:** ![vincent](https://avatars.discourse-cdn.com/v4/letter/v/e9bcb4/32.png) [@vincent](https://forum.inductiveautomation.com/u/vincent)\
**Post date:** [July 31, 2014, 3:05pm UTC](https://forum.inductiveautomation.com/t/connect-ignition-ua-server-to-a-second-ignition-ua-server/8828/3 "2014-07-31T15:05:52Z")

</div>

I did enter the local server adress which looks like 172.16.1.3  
Should I better give the public adress (193.248.xxx.xxx:4096) ?

If the endpoint adress were wrong, I don’t understand how I can still successfully connect and read opc tags with the Unified Automation OPC client ?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [July 31, 2014, 3:45pm UTC](https://forum.inductiveautomation.com/t/connect-ignition-ua-server-to-a-second-ignition-ua-server/8828/4 "2014-07-31T15:45:56Z")

</div>

In the console area of the gateway go to the levels tab and search for ‘ConnectionUtil’, turn that to TRACE, then let it try to connect. After a few attempts export the logs.bin.gz and either attach them here or send them to support.

---

<div class="post-metadata">

**Author:** ![vincent](https://avatars.discourse-cdn.com/v4/letter/v/e9bcb4/32.png) [@vincent](https://forum.inductiveautomation.com/u/vincent)\
**Post date:** [August 3, 2014, 7:52pm UTC](https://forum.inductiveautomation.com/t/connect-ignition-ua-server-to-a-second-ignition-ua-server/8828/5 "2014-08-03T19:52:07Z")

</div>

logs file attached as requested.  
[logs.bin.gz](https://us1.discourse-cdn.com/inductiveautomation/original/2X/f/f8d8094375e10dc555f6c7cc0394b7ed2f6d884c.gz) (390 KB)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [August 3, 2014, 9:53pm UTC](https://forum.inductiveautomation.com/t/connect-ignition-ua-server-to-a-second-ignition-ua-server/8828/6 "2014-08-03T21:53:28Z")

</div>

There’s an advanced setting when making the UA connection that allows you to override the endpoint address returned in the endpoint by the remote server - try setting that to the same value as the public IP you’re trying to connect to.

It looks like the server is bound to a 172.x.x.x address and is returning that in the endpoint and it’s not reachable remotely.

---

<div class="post-metadata">

**Author:** ![vincent](https://avatars.discourse-cdn.com/v4/letter/v/e9bcb4/32.png) [@vincent](https://forum.inductiveautomation.com/u/vincent)\
**Post date:** [August 5, 2014, 9:06pm UTC](https://forum.inductiveautomation.com/t/connect-ignition-ua-server-to-a-second-ignition-ua-server/8828/7 "2014-08-05T21:06:43Z")

</div>

Hello Kevin, that was it.

I’ve put the public address as override host an it has just connected.

Thank you for your support,

BR,

Vincent