# Connect Modbus type floating point value is missing

**URL:** <https://forum.inductiveautomation.com/t/connect-modbus-type-floating-point-value-is-missing/90000>\
**Category:** Ignition\
**Created:** [May 7, 2024, 7:57am UTC](https://forum.inductiveautomation.com/t/connect-modbus-type-floating-point-value-is-missing/90000 "2024-05-07T07:57:40Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![chumnan](https://avatars.discourse-cdn.com/v4/letter/c/5daacb/32.png) [@chumnan](https://forum.inductiveautomation.com/u/chumnan)\
**Post date:** [May 7, 2024, 7:57am UTC](https://forum.inductiveautomation.com/t/connect-modbus-type-floating-point-value-is-missing/90000/1 "2024-05-07T07:57:40Z")

</div>

Dear All  
I have problem about connect tag from power meter  
1.first step i use modscan for find value from power meter and i set display is(Floating Pt) value is OK  
2.I Config addressing on gateway  
3.But I read value from OPC Quick Client and value is missing

Help me please

 ![Screenshot 2024-05-07 144957](https://us1.discourse-cdn.com/inductiveautomation/original/3X/3/2/32013c82e67308fda3962290a9cdfaec0731f5e4.png)

 ![Screenshot 2024-05-07 144845](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/8/28e3dd78d783d696411ab96fa4935aa29111d798.png)

---

<div class="post-metadata">

**Author:** ![Andrii\_Ushchapovskyi](https://avatars.discourse-cdn.com/v4/letter/a/a3d4f5/32.png) [@Andrii\_Ushchapovskyi](https://forum.inductiveautomation.com/u/Andrii_Ushchapovskyi)\
**Post date:** [May 7, 2024, 8:16am UTC](https://forum.inductiveautomation.com/t/connect-modbus-type-floating-point-value-is-missing/90000/2 "2024-05-07T08:16:57Z")

</div>

I guess you should use "swap words" option for this device