# Connect to 5069 PLC through ENBT

**URL:** <https://forum.inductiveautomation.com/t/connect-to-5069-plc-through-enbt/97486>\
**Category:** Ignition\
**Created:** [October 18, 2024, 8:15pm UTC](https://forum.inductiveautomation.com/t/connect-to-5069-plc-through-enbt/97486 "2024-10-18T20:15:28Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![john.ackley](https://avatars.discourse-cdn.com/v4/letter/j/c6cbf5/32.png) [@john.ackley](https://forum.inductiveautomation.com/u/john.ackley)\
**Post date:** [October 18, 2024, 8:15pm UTC](https://forum.inductiveautomation.com/t/connect-to-5069-plc-through-enbt/97486/1 "2024-10-18T20:15:28Z")

</div>

I am trying to connect to a 5069-L320ER PLC through a 1756-ENBT card in a ControlLogix Chassis. The sub network ENBT card is in slot 3. The CompactLogix IP address is 192.168.55.10. I have tried a connection path of 1,3,2,192.168.55.10 and 1,3,2,192.168.55.10,1,0 and neither have worked. On the OPCUA Devices page of the Gateway it says connected, but when I try to open a quick client, there are no tags. Thank you for your help.

---

<div class="post-metadata">

**Author:** ![michael.flagler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.flagler/32/26272_2.png) [@michael.flagler](https://forum.inductiveautomation.com/u/michael.flagler)\
**Post date:** [October 18, 2024, 8:33pm UTC](https://forum.inductiveautomation.com/t/connect-to-5069-plc-through-enbt/97486/2 "2024-10-18T20:33:20Z")

</div>

I would think the connection path should just be:

```python
1,3,2,192.168.55.10

1 = Backplane
3 = Slot 3
2 = Ethernet Port
192.168.55.10 = CompactLogix PLC

```

Is the ENBT card in the same rack as the ethernet card you're connecting to in your IP address? Is the hostname on your driver configuration, that of the ethernet card/PLC in the ControlLogix PLC rack?

Also, just confirming that the CompactLogix and ENBT card in slot 3 are on the same subnet and physical network. If not, is there a proper router/NAT device and gateway IPs put in everything to properly connect the 2 together?