Hello,

I trying to connect to the Ingition’s OPC server using UAExpert (for the moment). I’m having problems.

I add “None” in the security poloicies. I also checked “Anonymous access allowed”. But is is not working.

I suspect I must change something in the “Bind Address” parameter. It is actually set to “localhost”. I want my server to accept any connection from the network.

Sone help would be very appreciated.

Thanks.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [June 3, 2020, 7:01pm UTC](https://forum.inductiveautomation.com/t/connect-uaexpert-to-opc-ua-server/35300/2 "2020-06-03T19:01:14Z")

</div>

Change the bind address to 0.0.0.0 and then restart the UA module or Ignition gateway.

---

<div class="post-metadata">

**Author:** ![vrautomation](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/vrautomation/32/11155_2.png) [@vrautomation](https://forum.inductiveautomation.com/u/vrautomation)\
**Post date:** [June 4, 2020, 12:18am UTC](https://forum.inductiveautomation.com/t/connect-uaexpert-to-opc-ua-server/35300/3 "2020-06-04T00:18:01Z")

</div>

It works… with security and authentication.

I’ve not been able to make it work without security and authentication… But it’s good.

Thanks.

---