i have an issue with a micrologix 1100 where it never connects an just shows that message any recommendation?

---

<div class="post-metadata">

**Author:** ![Transistor](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/transistor/32/3380_2.png) [@Transistor](https://forum.inductiveautomation.com/u/Transistor)\
**Post date:** [August 17, 2025, 8:23am UTC](https://forum.inductiveautomation.com/t/connecting-determining-protocol/109851/2 "2025-08-17T08:23:53Z")

</div>

Yes. Post your configuration so we can see what it is.

- Can you ping the PLC?
- Can you browse the PLC's web server. (I think it has one.)
- What is the network route between your Ignition gateway and the PLC?

Setup should be a matter of going to gateway's Config | OPC UA | Device Connections | Add new | select Allen-Bradley MicroLogix and enter the IP address.

Welcome to the forum.

---

<div class="post-metadata">

**Author:** ![crisdleon19](https://avatars.discourse-cdn.com/v4/letter/c/f4b2a3/32.png) [@crisdleon19](https://forum.inductiveautomation.com/u/crisdleon19)\
**Post date:** [August 17, 2025, 1:38pm UTC](https://forum.inductiveautomation.com/t/connecting-determining-protocol/109851/3 "2025-08-17T13:38:26Z")

</div>

yes i can ping the PLC, but no i cant access the web server, and here is the config, i have other devices that connected without any issue, so im a little puzzled as of why this one is giving me the headaches

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/2/c2740cb2a61a5547d91298e9055680df0be034e8.png)

and thank you for the welcome

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [August 17, 2025, 1:39pm UTC](https://forum.inductiveautomation.com/t/connecting-determining-protocol/109851/4 "2025-08-17T13:39:31Z")

</div>

Connection Path should probably be either `1,0` or blank.

---

<div class="post-metadata">

**Author:** ![crisdleon19](https://avatars.discourse-cdn.com/v4/letter/c/f4b2a3/32.png) [@crisdleon19](https://forum.inductiveautomation.com/u/crisdleon19)\
**Post date:** [August 17, 2025, 1:54pm UTC](https://forum.inductiveautomation.com/t/connecting-determining-protocol/109851/5 "2025-08-17T13:54:52Z")

</div>

> [@Kevin.Herron](#):
>
> `1,0`

I tried that, but still no success, i also tried accesing the port with telnet ip 44818 but no response whatsoever but the thing is that we are migrating a program form indusoft to ignition, and on indusoft they managed to get info from the plc hence they have connection

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [August 17, 2025, 1:56pm UTC](https://forum.inductiveautomation.com/t/connecting-determining-protocol/109851/6 "2025-08-17T13:56:39Z")

</div>

> [@crisdleon19](#):
>
> i also tried accesing the port with telnet ip 44818 but no response whatsoever

That usually points to an issue outside of Ignition. Firewall, wrong IP, device config, etc…

---

<div class="post-metadata">

**Author:** ![crisdleon19](https://avatars.discourse-cdn.com/v4/letter/c/f4b2a3/32.png) [@crisdleon19](https://forum.inductiveautomation.com/u/crisdleon19)\
**Post date:** [August 17, 2025, 1:57pm UTC](https://forum.inductiveautomation.com/t/connecting-determining-protocol/109851/7 "2025-08-17T13:57:47Z")

</div>

will try to check on that, just wanted to make sure that theres nothing more i can do from ignition

---

<div class="post-metadata">

**Author:** ![crisdleon19](https://avatars.discourse-cdn.com/v4/letter/c/f4b2a3/32.png) [@crisdleon19](https://forum.inductiveautomation.com/u/crisdleon19)\
**Post date:** [August 17, 2025, 1:58pm UTC](https://forum.inductiveautomation.com/t/connecting-determining-protocol/109851/8 "2025-08-17T13:58:57Z")

</div>

thanks for the help anyways, at least now I’m sure, where to look and where not to look

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [August 17, 2025, 5:29pm UTC](https://forum.inductiveautomation.com/t/connecting-determining-protocol/109851/9 "2025-08-17T17:29:27Z")

</div>

If the 1100 has old firmware, it may need to connect via port 2222.