Hello,

I would like to communicate with some B&R PLC that use presently a PVI driver.  
I cannot enable another communication on the PLC so I need to use this specific driver on the PLC, someone knows if this communication is modbus TCP compatible (same addresses)?  
thanking you in advance

Michel Feria

---

<div class="post-metadata">

**Author:** ![plo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/plo/32/33875_2.png) [@plo](https://forum.inductiveautomation.com/u/plo)\
**Post date:** [January 30, 2023, 11:46pm UTC](https://forum.inductiveautomation.com/t/connecting-ignition-to-b-r-plc/68884/2 "2023-01-30T23:46:04Z")

</div>

Hello michel\_feria,

Could you share your B&R PLC's Make, Model, Firmware Version ? It might help us find out more information on what your PLC supports. I would recommend contacting the B&R PLC manufacturer to confirm what protocols they support with your PLC Device.

But we have heard using Ignition's OPC UA Client connection to connect to the B&R's onboard UA Server

> [@Communication between B&R PLC and Ignition over OPC UA](https://forum.inductiveautomation.com/t/communication-between-b-r-plc-and-ignition-over-opc-ua/6017/1):
>
> Hi All, I am using the available Ethernet port of X201583 to connect B&R X20 PLC to Ignition over OPC-UA. Is is possible to connect B&R PLC X201583 to Ignition without using BC0087 module? Steps followed to connect the B&R PLC and Ignition without using BC0087 module are as follows. B&R PLC (Available Ethernet Port) ---------\>(Cat 5) Cable ---------\> Ignition PC I created the “New Device” clicking “Add New Device” I configured the B&R PLC’s IP address and Port number in the “Newly Created D…