# Connecting Ignition to device that support Ethernet/IP (without PLC)

**URL:** <https://forum.inductiveautomation.com/t/connecting-ignition-to-device-that-support-ethernet-ip-without-plc/35576>\
**Category:** Ignition\
**Created:** [June 12, 2020, 1:25am UTC](https://forum.inductiveautomation.com/t/connecting-ignition-to-device-that-support-ethernet-ip-without-plc/35576 "2020-06-12T01:25:56Z")\
**Posts on this page:** 14\
**Page:** 1

<div class="post-metadata">

**Author:** ![maruthi.addala](https://avatars.discourse-cdn.com/v4/letter/m/b2d939/32.png) [@maruthi.addala](https://forum.inductiveautomation.com/u/maruthi.addala)\
**Post date:** [June 12, 2020, 1:25am UTC](https://forum.inductiveautomation.com/t/connecting-ignition-to-device-that-support-ethernet-ip-without-plc/35576/1 "2020-06-12T01:25:56Z")

</div>

Hello Experts,

i am looking for some guidance on how can i connect IGNITION to device without PLC, that supports Ethernet/IP protocol.

In my case its a Leak tester that supports Ethernet/IP.

i found some forums, but did not actually help.

Thanks.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [June 12, 2020, 3:12am UTC](https://forum.inductiveautomation.com/t/connecting-ignition-to-device-that-support-ethernet-ip-without-plc/35576/2 "2020-06-12T03:12:24Z")

</div>

Ignition does not have a driver for this.

I don’t know if @pturmel’s driver can do this or not, maybe he can chime in.

---

<div class="post-metadata">

**Author:** ![maruthi.addala](https://avatars.discourse-cdn.com/v4/letter/m/b2d939/32.png) [@maruthi.addala](https://forum.inductiveautomation.com/u/maruthi.addala)\
**Post date:** [June 12, 2020, 11:53am UTC](https://forum.inductiveautomation.com/t/connecting-ignition-to-device-that-support-ethernet-ip-without-plc/35576/3 "2020-06-12T11:53:29Z")

</div>

i kind of found this forum from pturmel.. but i am not clear really..

> [@Ignition to EtherNet/IP without a PLC](http://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/2):
>
> That sounds interesting… [Ethernet/IP Class 1 Communications](https://inductiveautomation.com/moduleshowcase/module/automation-professionals-llc-ethernetip-class-1-communications) (:

Also- Do you think if using any Modules that convert from Ethernet/IP to Modbus TCP will help me to connect from ignition...?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [June 12, 2020, 1:18pm UTC](https://forum.inductiveautomation.com/t/connecting-ignition-to-device-that-support-ethernet-ip-without-plc/35576/4 "2020-06-12T13:18:15Z")

</div>

If the leak tester has an EDS file that you can share with me, I can tell pretty quickly if my module will support it. Or provide a link to the product documentation that I can examine.

---

<div class="post-metadata">

**Author:** ![maruthi.addala](https://avatars.discourse-cdn.com/v4/letter/m/b2d939/32.png) [@maruthi.addala](https://forum.inductiveautomation.com/u/maruthi.addala)\
**Post date:** [June 12, 2020, 3:43pm UTC](https://forum.inductiveautomation.com/t/connecting-ignition-to-device-that-support-ethernet-ip-without-plc/35576/5 "2020-06-12T15:43:02Z")

</div>

Product that supports Profinet and Ethernet/IP: [https://www.leakmasterusa.com/ultraflow-v3-rt/](https://www.leakmasterusa.com/ultraflow-v3-rt/)

I have other leaktester I think it supports Modbus over TCP (series 700)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [June 12, 2020, 5:51pm UTC](https://forum.inductiveautomation.com/t/connecting-ignition-to-device-that-support-ethernet-ip-without-plc/35576/6 "2020-06-12T17:51:35Z")

</div>

“Slave mode” is almost certainly the mode I would need. If you can get the EDS file from their support group I can take a closer look. The user manual might have useful information, too.

---

<div class="post-metadata">

**Author:** ![maruthi.addala](https://avatars.discourse-cdn.com/v4/letter/m/b2d939/32.png) [@maruthi.addala](https://forum.inductiveautomation.com/u/maruthi.addala)\
**Post date:** [June 12, 2020, 7:50pm UTC](https://forum.inductiveautomation.com/t/connecting-ignition-to-device-that-support-ethernet-ip-without-plc/35576/7 "2020-06-12T19:50:10Z")

</div>

Below is the reply i got from the Vendor.

"On the UFv3 RT model our device acts as a slave/adapter. In order for a gateway to work, it must act as the Ethernet/IP master/scanner.

Use this link to find the module you need, for the Ethernet/IP (UFv3 side) you need to choose “Ethernet/IP/Scanner/Master” and select the protocol you need on your side. [https://www.anybus.com/products/gateway-index/anybus-xgateway](https://www.anybus.com/products/gateway-index/anybus-xgateway)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [June 13, 2020, 2:04am UTC](https://forum.inductiveautomation.com/t/connecting-ignition-to-device-that-support-ethernet-ip-without-plc/35576/8 "2020-06-13T02:04:04Z")

</div>

The premium version of my module acts as a master/scanner. The anybus would not be needed. However, using the anybus would probably be cheaper than my module. Unless you had more than one or two of these leak testers.

If the vendor has instructions (like, in a user manual) on how to use their product with a modern Allen-Bradley processor (Logix), the instructions would be sufficient to figure out how to use it with my scanner module.

---

<div class="post-metadata">

**Author:** ![maruthi.addala](https://avatars.discourse-cdn.com/v4/letter/m/b2d939/32.png) [@maruthi.addala](https://forum.inductiveautomation.com/u/maruthi.addala)\
**Post date:** [June 13, 2020, 2:00pm UTC](https://forum.inductiveautomation.com/t/connecting-ignition-to-device-that-support-ethernet-ip-without-plc/35576/9 "2020-06-13T14:00:58Z")

</div>

well, the thing is I might have other devices that has Ethernet/IP protocols, so instead of buying any bus for every device, its worth to know that ur Module(Premium) version works. Also does ur Module supports other protocols such as Profinet…?.

can you please provide the link to your Module…?  
Also what is the difference between your Modules and any other OPC servers softwares(such as Kepware in the market).

---

<div class="post-metadata">

**Author:** ![bmusson](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/bmusson/32/87530_2.png) [@bmusson](https://forum.inductiveautomation.com/u/bmusson)\
**Post date:** [June 13, 2020, 2:23pm UTC](https://forum.inductiveautomation.com/t/connecting-ignition-to-device-that-support-ethernet-ip-without-plc/35576/10 "2020-06-13T14:23:56Z")

</div>

Phil should be the one to explain what’s unique about his module, but I just wanted to chime in and give a personal recommendation for his product. Really great stuff.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [June 13, 2020, 5:36pm UTC](https://forum.inductiveautomation.com/t/connecting-ignition-to-device-that-support-ethernet-ip-without-plc/35576/11 "2020-06-13T17:36:37Z")

</div>

> [@maruthi.addala](#):
>
> Also does ur Module supports other protocols such as Profinet…?.

No. Ethernet/IP only.

> [@maruthi.addala](#):
>
> can you please provide the link to your Module…?

A summary is in Inductive Automation's [Showcase](https://inductiveautomation.com/moduleshowcase/module/automation-professionals-llc-ethernetip-class-1-communications). Clicking on the "Buy this module" link actually takes you to [my own site](https://www.automation-pros.com/modulesales.html) where all of my modules are available. The downloads are there.

> [@maruthi.addala](#):
>
> Also what is the difference between your Modules and any other OPC servers

My module is an OPC/UA _ **driver** _ specifically for use in Ignition, and runs as part of your Ignition gateway. It is not a separate process--not a separate OPC server at all--and does not require Windows.

---

<div class="post-metadata">

**Author:** ![maruthi.addala](https://avatars.discourse-cdn.com/v4/letter/m/b2d939/32.png) [@maruthi.addala](https://forum.inductiveautomation.com/u/maruthi.addala)\
**Post date:** [June 14, 2020, 12:17am UTC](https://forum.inductiveautomation.com/t/connecting-ignition-to-device-that-support-ethernet-ip-without-plc/35576/12 "2020-06-14T00:17:48Z")

</div>

Thanks pturmel.

---

<div class="post-metadata">

**Author:** ![melwadeya](https://avatars.discourse-cdn.com/v4/letter/m/ed8c4c/32.png) [@melwadeya](https://forum.inductiveautomation.com/u/melwadeya)\
**Post date:** [December 22, 2023, 11:38am UTC](https://forum.inductiveautomation.com/t/connecting-ignition-to-device-that-support-ethernet-ip-without-plc/35576/13 "2023-12-22T11:38:02Z")

</div>

@pturmel does your module work in Ignition Edge (V8.1.17)?

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [December 22, 2023, 11:43am UTC](https://forum.inductiveautomation.com/t/connecting-ignition-to-device-that-support-ethernet-ip-without-plc/35576/14 "2023-12-22T11:43:07Z")

</div>

No 3rd party modules are allowed in Edge.