# Connecting Proface STM6000

**URL:** <https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758>\
**Category:** General Discussion\
**Created:** [February 4, 2026, 10:43am UTC](https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758 "2026-02-04T10:43:12Z")\
**Posts on this page:** 16\
**Page:** 1

<div class="post-metadata">

**Author:** ![olivier.roberge](https://avatars.discourse-cdn.com/v4/letter/o/6f9a4e/32.png) [@olivier.roberge](https://forum.inductiveautomation.com/u/olivier.roberge)\
**Post date:** [February 4, 2026, 10:43am UTC](https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758/1 "2026-02-04T10:43:13Z")

</div>

Hello!

I’m trying to connect a Proface STM6000 to Ignition.

This system is OPC-UA server. I can check the connexion succesfully using UAExpert.

But the connexion to Ignition is not stable. Maybe a link configuration problem?

Has anyone already worked on this product?

Thanks for your help!

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 4, 2026, 2:14pm UTC](https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758/2 "2026-02-04T14:14:15Z")

</div>

What version of Ignition are you using? What's does "not stable" mean? What's in the logs?

---

<div class="post-metadata">

**Author:** ![olivier.roberge](https://avatars.discourse-cdn.com/v4/letter/o/6f9a4e/32.png) [@olivier.roberge](https://forum.inductiveautomation.com/u/olivier.roberge)\
**Post date:** [February 5, 2026, 9:09am UTC](https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758/3 "2026-02-05T09:09:45Z")

</div>

Hello Kevin.

I'm working on the trial version of Ignition.

I've already worked successfully on B&R equipment.

Now I try to connect our Proface STM6000.

You will find attached pictures describing my project:

- The STM6000 configuration (OPC-UA server on port 4840).

- The result on UAExpert (it works fine).

- The result on Ignition trial (connection is not stable, it switches slowly between "connected" and "not connected" states).

I used Modbus TCP driver, but maybe this is a bad choice.

Could you please help me on this subject?

Thanks!

 ![STM6000_Config](https://us1.discourse-cdn.com/inductiveautomation/original/3X/8/9/89d2ff389d8c7b8ba0c05f30eccf18c897a4d4c9.png)

 ![UAExpert](https://us1.discourse-cdn.com/inductiveautomation/original/3X/4/7/476cf853b748182cd802d28751588650a55a10e0.png)

 ![Ignition_04](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/2/729e49731e8ef40eee316f0f0cb8d2e8235501df.png)

---

<div class="post-metadata">

**Author:** ![David\_Stone](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/david_stone/32/79749_2.png) [@David\_Stone](https://forum.inductiveautomation.com/u/David_Stone)\
**Post date:** [February 5, 2026, 9:20am UTC](https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758/4 "2026-02-05T09:20:24Z")

</div>

> [@olivier.roberge](#):
>
> Modbus TCP driver,

If you are using modbus TCP, why are you showing us OPC-UA settings?

Your connection has nothing set up for OPC-UA, if you were intending to use OPC-UA, maybe follow the OPC-UA connection documentation?

> **[OPC UA Client Connection Settings | Ignition User Manual](https://www.docs.inductiveautomation.com/docs/8.1/ignition-modules/opc-ua/opc-ua-client-connection-settings)**
>
> Configuring an OPC Client Connection

---

<div class="post-metadata">

**Author:** ![olivier.roberge](https://avatars.discourse-cdn.com/v4/letter/o/6f9a4e/32.png) [@olivier.roberge](https://forum.inductiveautomation.com/u/olivier.roberge)\
**Post date:** [February 5, 2026, 10:33am UTC](https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758/5 "2026-02-05T10:33:25Z")

</div>

I tried OPCUA configuration as you are suggesting.

In this case connexion is stable, but I cannot see any variable in the browser (no security option selected on both side).

---

<div class="post-metadata">

**Author:** ![David\_Stone](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/david_stone/32/79749_2.png) [@David\_Stone](https://forum.inductiveautomation.com/u/David_Stone)\
**Post date:** [February 5, 2026, 10:35am UTC](https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758/6 "2026-02-05T10:35:31Z")

</div>

Can you show us the browser?

---

<div class="post-metadata">

**Author:** ![olivier.roberge](https://avatars.discourse-cdn.com/v4/letter/o/6f9a4e/32.png) [@olivier.roberge](https://forum.inductiveautomation.com/u/olivier.roberge)\
**Post date:** [February 5, 2026, 11:48am UTC](https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758/7 "2026-02-05T11:48:43Z")

</div>

![STM6000_OPCUA_01](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/1/d1ff8a2abf2d6f4ffd6d262f113e90be5ff5b5e5.png)

 ![STM6000_OPCUA_02](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/5/75dc41ba0c3662ee061405258eb1400eb0b4c3ea.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 5, 2026, 12:17pm UTC](https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758/8 "2026-02-05T12:17:20Z")

</div>

It would be interesting to see a screenshot of the attributes and references pane while the Objects node is selected in UaExpert.

Based on the name of those variables (Alarm...) it might be possible this server's data model is using only non-hierarchical reference types, which Ignition does not browse for.

---

<div class="post-metadata">

**Author:** ![olivier.roberge](https://avatars.discourse-cdn.com/v4/letter/o/6f9a4e/32.png) [@olivier.roberge](https://forum.inductiveautomation.com/u/olivier.roberge)\
**Post date:** [February 6, 2026, 8:53am UTC](https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758/9 "2026-02-06T08:53:46Z")

</div>

![Node_01](https://us1.discourse-cdn.com/inductiveautomation/original/3X/9/7/9704290fd7b6fa52604334cc7f9824d918fc9978.png)

 ![Node_02](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/8/d89ab7d816aa20d6e4907f50652992ca228f2265.png)

Could you confirm your analyze please? And how can I access the variables from Ignition?

---

<div class="post-metadata">

**Author:** ![David\_Stone](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/david_stone/32/79749_2.png) [@David\_Stone](https://forum.inductiveautomation.com/u/David_Stone)\
**Post date:** [February 6, 2026, 9:58am UTC](https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758/10 "2026-02-06T09:58:46Z")

</div>

Make a new standard tag:

- Value Source: `OPC`
- OPC Server: `STM6000`
- Path: `ns=2;s=TK1_Temperature`
- Data Type: `Integer`

See if that works?

---

<div class="post-metadata">

**Author:** ![olivier.roberge](https://avatars.discourse-cdn.com/v4/letter/o/6f9a4e/32.png) [@olivier.roberge](https://forum.inductiveautomation.com/u/olivier.roberge)\
**Post date:** [February 6, 2026, 12:41pm UTC](https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758/11 "2026-02-06T12:41:12Z")

</div>

Yes, perfect.

Thanks for your help!

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 6, 2026, 2:21pm UTC](https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758/12 "2026-02-06T14:21:31Z")

</div>

You can access them manually like @David_Stone suggested.

I need you to get a screenshot while you've selected the Objects node in UaExpert to further analyze. Make sure all the references in the references pane are visible once you've done so.

---

<div class="post-metadata">

**Author:** ![olivier.roberge](https://avatars.discourse-cdn.com/v4/letter/o/6f9a4e/32.png) [@olivier.roberge](https://forum.inductiveautomation.com/u/olivier.roberge)\
**Post date:** [February 6, 2026, 3:18pm UTC](https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758/13 "2026-02-06T15:18:57Z")

</div>

![Capture d’écran (17)](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/b/dba871912c2ce32a8394c5a1747d417817f215e7.png)

 ![Capture d’écran (16)](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/2/220582e85039bd130d3b78b4bdabcf2c2f2ffde3.png)

 ![Capture d’écran (15)](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/1/c1f1dac47b34dea616dcb5e6cae07813f0318df7.png)

Is this sufficient?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 6, 2026, 3:22pm UTC](https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758/14 "2026-02-06T15:22:31Z")

</div>

Yeah, interesting. Something must be going wrong during the browse. Would need a Wireshark capture of the traffic between Ignition and that server to further diagnose. The OPC UA connection would have to be made without security.

If this is something you want to pursue and don't feel comfortable with Wireshark you can contact support and they can help you with it.

My guess is something like... that server has 1446 references from the Objects folder... when we browse, we follow up with a read for a few attributes of each of the referenced nodes... servers often do not include the information in the address space about the maximum number of reads/writes/operations for each service... so maybe we're following up with a read that is too large. There is a "Max Per Operation" advanced setting on the OPC UA connections in Ignition that you could lower to something like 100 to test this theory.

---

<div class="post-metadata">

**Author:** ![olivier.roberge](https://avatars.discourse-cdn.com/v4/letter/o/6f9a4e/32.png) [@olivier.roberge](https://forum.inductiveautomation.com/u/olivier.roberge)\
**Post date:** [February 9, 2026, 2:17pm UTC](https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758/15 "2026-02-09T14:17:21Z")

</div>

I performed a few more tests… The data the customer wants to receive are managed under boolean format. I changed this to send only words, and with this modifcation the browser works perfectly.

Thanks!

---

<div class="post-metadata">

**Author:** ![olivier.roberge](https://avatars.discourse-cdn.com/v4/letter/o/6f9a4e/32.png) [@olivier.roberge](https://forum.inductiveautomation.com/u/olivier.roberge)\
**Post date:** [February 9, 2026, 3:29pm UTC](https://forum.inductiveautomation.com/t/connecting-proface-stm6000/113758/16 "2026-02-09T15:29:37Z")

</div>

Wrong analyze. I made a mistake, sorry. Proface system is able to manage about 800 tags, boolean and words.