# ControlLogix Connection Path via 2 ENBTs

**URL:** <https://forum.inductiveautomation.com/t/controllogix-connection-path-via-2-enbts/71920>\
**Category:** Ignition\
**Created:** [March 31, 2023, 7:55pm UTC](https://forum.inductiveautomation.com/t/controllogix-connection-path-via-2-enbts/71920 "2023-03-31T19:55:28Z")\
**Posts on this page:** 11\
**Page:** 1

<div class="post-metadata">

**Author:** ![Joe\_Bonhage](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/joe_bonhage/32/45543_2.png) [@Joe\_Bonhage](https://forum.inductiveautomation.com/u/Joe_Bonhage)\
**Post date:** [March 31, 2023, 7:55pm UTC](https://forum.inductiveautomation.com/t/controllogix-connection-path-via-2-enbts/71920/1 "2023-03-31T19:55:28Z")

</div>

Hello!  
Looking for help on establishing a connection path to a L61 controller thru ENBT gateways.  
I have already connected to a PLC5 via DHRIO in slot 0 so I know I am close but cannot get to the L61.

Here's is what I have so far that (that is not working)  
1,2,10.10.10.50,1,1,0  
(backplane,port,target,backplane,port,target)

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/1/6/16309e5c2850f57e9ebb8273740a3510b9dddc09.png)

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/b/e/be8aec114201b9ef3002015136444afcec6c511d.png)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [March 31, 2023, 8:02pm UTC](https://forum.inductiveautomation.com/t/controllogix-connection-path-via-2-enbts/71920/2 "2023-03-31T20:02:33Z")

</div>

Try `1,2,3,10.10.10.50,1,0` or `1,2,4,10.10.10.50,1,0`

In my new driver it would be `slot 2 port 3 10.10.10.50 slot 0` or `slot 2 port 4 10.10.10.50 slot 0` fwiw.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 31, 2023, 8:32pm UTC](https://forum.inductiveautomation.com/t/controllogix-connection-path-via-2-enbts/71920/3 "2023-03-31T20:32:03Z")

</div>

Your screenshot highlights a node under 10.10.10.11, not 10.10.10.50 - intentional?

---

<div class="post-metadata">

**Author:** ![Joe\_Bonhage](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/joe_bonhage/32/45543_2.png) [@Joe\_Bonhage](https://forum.inductiveautomation.com/u/Joe_Bonhage)\
**Post date:** [March 31, 2023, 8:35pm UTC](https://forum.inductiveautomation.com/t/controllogix-connection-path-via-2-enbts/71920/4 "2023-03-31T20:35:35Z")

</div>

@pturmel I did try both of them but didn't work.  
@Kevin.Herron I guess I'm a bit confused here. 10.10.10.50 is the IP of the 2nd ENBT card (slot 2)  
Then when browsing under that card, the controller is under 10.10.10.11 (slot 0)

---

<div class="post-metadata">

**Author:** ![Joe\_Bonhage](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/joe_bonhage/32/45543_2.png) [@Joe\_Bonhage](https://forum.inductiveautomation.com/u/Joe_Bonhage)\
**Post date:** [March 31, 2023, 8:36pm UTC](https://forum.inductiveautomation.com/t/controllogix-connection-path-via-2-enbts/71920/5 "2023-03-31T20:36:35Z")

</div>

I highlighted the L61 controller I'm trying to get the tags. Thanks for the help!

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [March 31, 2023, 8:41pm UTC](https://forum.inductiveautomation.com/t/controllogix-connection-path-via-2-enbts/71920/6 "2023-03-31T20:41:01Z")

</div>

Whoops! Right. Where I showed `10.10.10.50`, use `10.10.10.11`. No reference to the first ENBT's address is required. You are reaching it by its slot address, not its IP address.

---

<div class="post-metadata">

**Author:** ![Joe\_Bonhage](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/joe_bonhage/32/45543_2.png) [@Joe\_Bonhage](https://forum.inductiveautomation.com/u/Joe_Bonhage)\
**Post date:** [March 31, 2023, 8:54pm UTC](https://forum.inductiveautomation.com/t/controllogix-connection-path-via-2-enbts/71920/7 "2023-03-31T20:54:05Z")

</div>

tried both these but didn't work:  
1,2,4,10.10.10.11,1,0  
1,2,3,10.10.10.11,1,0

did another picture as it's still fuzzy on the comms path.  
First hits 10.88.50.19, then go to the 2nd ENBT card (10.10.10.50), then goes to 10.10.10.11 which the L61 resides

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/8/0/80a2462bac184ca5e2a1ae8a2887d419589989fc.png)

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/a/f/afb6cb8f33292c104dca02116745a34cef7f558a.png)

---

<div class="post-metadata">

**Author:** ![Joe\_Bonhage](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/joe_bonhage/32/45543_2.png) [@Joe\_Bonhage](https://forum.inductiveautomation.com/u/Joe_Bonhage)\
**Post date:** [March 31, 2023, 8:58pm UTC](https://forum.inductiveautomation.com/t/controllogix-connection-path-via-2-enbts/71920/8 "2023-03-31T20:58:09Z")

</div>

this is what the drive looks like now but not connecting -- trying both 1,2,3 and 1,2,4 to start

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/b/c/bcb2c01ad7b4ae8c0cd1ccd65481c2bb27943f95.png)

---

<div class="post-metadata">

**Author:** ![Joe\_Bonhage](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/joe_bonhage/32/45543_2.png) [@Joe\_Bonhage](https://forum.inductiveautomation.com/u/Joe_Bonhage)\
**Post date:** [March 31, 2023, 8:59pm UTC](https://forum.inductiveautomation.com/t/controllogix-connection-path-via-2-enbts/71920/9 "2023-03-31T20:59:42Z")

</div>

got it working!  
Final answer: 1,2,2,10.10.10.11,1,0  
with the host name 10.88.50.19

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [March 31, 2023, 9:00pm UTC](https://forum.inductiveautomation.com/t/controllogix-connection-path-via-2-enbts/71920/10 "2023-03-31T21:00:04Z")

</div>

Well, I guessed wrong that port A would have #3 or #4. I just looked it up in the EDS file, and it is port #2. {Backplanes are always port #1.}

So: `1,2,2,10.10.10.11,1,0`

---

<div class="post-metadata">

**Author:** ![Joe\_Bonhage](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/joe_bonhage/32/45543_2.png) [@Joe\_Bonhage](https://forum.inductiveautomation.com/u/Joe_Bonhage)\
**Post date:** [March 31, 2023, 9:01pm UTC](https://forum.inductiveautomation.com/t/controllogix-connection-path-via-2-enbts/71920/11 "2023-03-31T21:01:06Z")

</div>

Yes, thank you!!