# ControlLogix device shows Disconnected with EIP indiction

**URL:** <https://forum.inductiveautomation.com/t/controllogix-device-shows-disconnected-with-eip-indiction/4882>\
**Category:** Ignition\
**Created:** [July 25, 2012, 3:49pm UTC](https://forum.inductiveautomation.com/t/controllogix-device-shows-disconnected-with-eip-indiction/4882 "2012-07-25T15:49:20Z")\
**Posts on this page:** 13\
**Page:** 1

<div class="post-metadata">

**Author:** ![Douglas](https://avatars.discourse-cdn.com/v4/letter/d/a6a055/32.png) [@Douglas](https://forum.inductiveautomation.com/u/Douglas)\
**Post date:** [July 25, 2012, 3:49pm UTC](https://forum.inductiveautomation.com/t/controllogix-device-shows-disconnected-with-eip-indiction/4882/1 "2012-07-25T15:49:20Z")

</div>

So I am getting this problem where I know the PLC is connected properly but Ignition will not talk to the device.

I’m using a ControlLogix5555 PLC.

I’ll copy and paste what the support center on the website says.

[quote]  
Problem  
ControlLogix device shows Disconnected with EIP Protocol indication. The Ignition driver will not fully connect or browse the processor.  
When the A-B Processor Sercurity utility is used it blocks reading the processor edit number as wel as browse operations.

Resolution  
Currently, turning off the processor security is the only way. If the ControlLogix driver is connected and then the security is turned on, it will work. This is risky because if the connection is lost, it will not reconnect until the processor security is turned off.[/quote]

Now how do I turn off processor security so I can connect to this device? Where is this toggled?

Thanks,

Doug

---

<div class="post-metadata">

**Author:** ![Douglas](https://avatars.discourse-cdn.com/v4/letter/d/a6a055/32.png) [@Douglas](https://forum.inductiveautomation.com/u/Douglas)\
**Post date:** [July 25, 2012, 5:00pm UTC](https://forum.inductiveautomation.com/t/controllogix-device-shows-disconnected-with-eip-indiction/4882/2 "2012-07-25T17:00:53Z")

</div>

So I found the CPU security utility and figured out how to disable processor security but it was already disabled. I tried enabling it and then disabling it and still no change with Ignition.

Still getting:

"Disconnected

Protocol: EIP"

Any guidance would be greatly appreciated.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [July 25, 2012, 5:03pm UTC](https://forum.inductiveautomation.com/t/controllogix-device-shows-disconnected-with-eip-indiction/4882/3 "2012-07-25T17:03:23Z")

</div>

What version of Ignition are you on? Can you export your logs from the Console area on the gateway and send them in?

---

<div class="post-metadata">

**Author:** ![Douglas](https://avatars.discourse-cdn.com/v4/letter/d/a6a055/32.png) [@Douglas](https://forum.inductiveautomation.com/u/Douglas)\
**Post date:** [July 25, 2012, 5:18pm UTC](https://forum.inductiveautomation.com/t/controllogix-device-shows-disconnected-with-eip-indiction/4882/4 "2012-07-25T17:18:59Z")

</div>

I am on Version 7.5.1 and I’ll attach my log file to this post.  
[logs[1].bin.gz](https://us1.discourse-cdn.com/inductiveautomation/original/2X/2/255564cd99e950aa4e86c39cb6cc46b681f126ea.gz) (78.2 KB)

---

<div class="post-metadata">

**Author:** ![thechtman](https://avatars.discourse-cdn.com/v4/letter/t/e56c9b/32.png) [@thechtman](https://forum.inductiveautomation.com/u/thechtman)\
**Post date:** [July 25, 2012, 5:26pm UTC](https://forum.inductiveautomation.com/t/controllogix-device-shows-disconnected-with-eip-indiction/4882/5 "2012-07-25T17:26:52Z")

</div>

Use the RSLogix 5000 Software CPU Lock Security Tool

If you can use RSLogix 5000 to connect to the processor with entering a password, then it is not the issue.

---

<div class="post-metadata">

**Author:** ![Douglas](https://avatars.discourse-cdn.com/v4/letter/d/a6a055/32.png) [@Douglas](https://forum.inductiveautomation.com/u/Douglas)\
**Post date:** [July 25, 2012, 5:34pm UTC](https://forum.inductiveautomation.com/t/controllogix-device-shows-disconnected-with-eip-indiction/4882/6 "2012-07-25T17:34:07Z")

</div>

[quote=“thechtman”]Use the RSLogix 5000 Software CPU Lock Security Tool

If you can use RSLogix 5000 to connect to the processor with entering a password, then it is not the issue.[/quote]

Don’t you mean “If you can use RSLogix 5000 to connect to the processor without entering a password”

It says the processor security should be off meaning I would want it in the state where I do not need to enter a password. Or am I mistaken?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [July 25, 2012, 5:37pm UTC](https://forum.inductiveautomation.com/t/controllogix-device-shows-disconnected-with-eip-indiction/4882/7 "2012-07-25T17:37:28Z")

</div>

Are you still trying to use “EXILE-C306C70C4!AB\_ETHIP-1\10.28.210.110\Backplane\1” as your hostname?

---

<div class="post-metadata">

**Author:** ![Douglas](https://avatars.discourse-cdn.com/v4/letter/d/a6a055/32.png) [@Douglas](https://forum.inductiveautomation.com/u/Douglas)\
**Post date:** [July 25, 2012, 6:03pm UTC](https://forum.inductiveautomation.com/t/controllogix-device-shows-disconnected-with-eip-indiction/4882/8 "2012-07-25T18:03:21Z")

</div>

No, I was just trying different host names when it wasn’t working.

I now just have the IP address of the device in the hostname field.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [July 25, 2012, 6:05pm UTC](https://forum.inductiveautomation.com/t/controllogix-device-shows-disconnected-with-eip-indiction/4882/9 "2012-07-25T18:05:06Z")

</div>

Can you call into support some time today and let them take a look? There’s nothing obvious showing up in the logs.

---

<div class="post-metadata">

**Author:** ![Douglas](https://avatars.discourse-cdn.com/v4/letter/d/a6a055/32.png) [@Douglas](https://forum.inductiveautomation.com/u/Douglas)\
**Post date:** [July 25, 2012, 6:14pm UTC](https://forum.inductiveautomation.com/t/controllogix-device-shows-disconnected-with-eip-indiction/4882/10 "2012-07-25T18:14:47Z")

</div>

Yeah of course, thanks for your help.

---

<div class="post-metadata">

**Author:** ![thechtman](https://avatars.discourse-cdn.com/v4/letter/t/e56c9b/32.png) [@thechtman](https://forum.inductiveautomation.com/u/thechtman)\
**Post date:** [July 25, 2012, 6:31pm UTC](https://forum.inductiveautomation.com/t/controllogix-device-shows-disconnected-with-eip-indiction/4882/11 "2012-07-25T18:31:26Z")

</div>

About the security you are correct. If no password is required, then security is not turned on. By requiring a password, it locks access to the processor. This includes RSLogix and any other system reading tags.

A side thought: is the slot or connection path set correctly?

---

<div class="post-metadata">

**Author:** ![Douglas](https://avatars.discourse-cdn.com/v4/letter/d/a6a055/32.png) [@Douglas](https://forum.inductiveautomation.com/u/Douglas)\
**Post date:** [July 25, 2012, 8:45pm UTC](https://forum.inductiveautomation.com/t/controllogix-device-shows-disconnected-with-eip-indiction/4882/12 "2012-07-25T20:45:13Z")

</div>

The Processor is in slot 1 and I put that in the “Slot Number” field.

I don’t have anything in the “Connection Path” field as I figured I just ignore that if I have the “Slot Number” field filled in.

I wasn’t sure where to find the connection path. It says “See documentation for more details” but I wasn’t sure if that was PLC documentation or Ignition documentation.

How can I find my connection path?

Cheers

---

<div class="post-metadata">

**Author:** ![thechtman](https://avatars.discourse-cdn.com/v4/letter/t/e56c9b/32.png) [@thechtman](https://forum.inductiveautomation.com/u/thechtman)\
**Post date:** [July 25, 2012, 9:49pm UTC](https://forum.inductiveautomation.com/t/controllogix-device-shows-disconnected-with-eip-indiction/4882/13 "2012-07-25T21:49:52Z")

</div>

Yes, we are behind on getting the connection path data into the manual. It will be coming. For now look at this forum post. [http://www.inductiveautomation.com/forum/viewtopic.php?f=70&t=5228&p=15005&hilit=ControlLogix+Connection+Path#p15005](http://www.inductiveautomation.com/forum/viewtopic.php?f=70&t=5228&p=15005&hilit=ControlLogix+Connection+Path#p15005)

Yes, if you are connecting using a ENBT or other Ethernet module to the chassis containing the processor, then you don’t need to enter a connection path. Just set the slot number like you are doing.

Sounds like a call into tech support is probably the best way to narrow in on the problem.