**Author:** ![tbennett.tdc](https://avatars.discourse-cdn.com/v4/letter/t/54ee81/32.png) [@tbennett.tdc](https://forum.inductiveautomation.com/u/tbennett.tdc)\
**Post date:** [July 29, 2025, 5:52pm UTC](https://forum.inductiveautomation.com/t/create-easy-chart-pen-tags-from-udt-in-template/109096/1 "2025-07-29T17:52:42Z")

</div>

I've seen similar posts and answers that describe how to pass Easy Chart tags to a popup window. This seems straightforward enough, but I'd like to populate a simple Easy Chart in a Template from the 2 historical tags that are part of the Template's underlying UDT Tag. This seems like something that should be able to be done. Any ideas?

---

<div class="post-metadata">

**Author:** ![robertm](https://avatars.discourse-cdn.com/v4/letter/r/ea5d25/32.png) [@robertm](https://forum.inductiveautomation.com/u/robertm)\
**Post date:** [July 30, 2025, 12:17am UTC](https://forum.inductiveautomation.com/t/create-easy-chart-pen-tags-from-udt-in-template/109096/2 "2025-07-30T00:17:49Z")

</div>

Easiest for me is to create internal custom properties on the template, bind them to the UDT tags, then use cell binding on the easy charts pen data set to populate what you need by binding to the custom properties.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [July 30, 2025, 2:03am UTC](https://forum.inductiveautomation.com/t/create-easy-chart-pen-tags-from-udt-in-template/109096/3 "2025-07-30T02:03:34Z")

</div>

I responded in the other topic:

> [@Pass tag history path to easy chart popup](https://forum.inductiveautomation.com/t/pass-tag-history-path-to-easy-chart-popup/53684/13):
>
> Yes. In the template, add an internal custom property of type Dataset, and populate it with the typical content for an EasyChart's tagPens property. Then use cell bindings in that template to inject the dynamic tag paths into that dataset. On your click or other event that opens the popup, pass that entire dataset as a window parameter into the popup. In the popup, use a property binding on the EasyChart to pull the root container named parameter into the tagPens property.

(In the future, do not double-post. Per [the rules](https://forum.inductiveautomation.com/faq).)

---

<div class="post-metadata">

**Author:** ![tbennett.tdc](https://avatars.discourse-cdn.com/v4/letter/t/54ee81/32.png) [@tbennett.tdc](https://forum.inductiveautomation.com/u/tbennett.tdc)\
**Post date:** [July 30, 2025, 3:41pm UTC](https://forum.inductiveautomation.com/t/create-easy-chart-pen-tags-from-udt-in-template/109096/4 "2025-07-30T15:41:39Z")

</div>

I'm sorry for double posting.

I saw what the other reply said but it is not the answer to my question. I don't want to create the pen tags when I open a popup, but rather when the instance of the template is created, or just a property binding that selects the database tag based on the underlying UDT tags. If the chart provides access to the historical database tags, I'd like to be able to directly, or indirectly, access the tag path to that, just like I can to any tag or property.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [July 30, 2025, 3:55pm UTC](https://forum.inductiveautomation.com/t/create-easy-chart-pen-tags-from-udt-in-template/109096/5 "2025-07-30T15:55:52Z")

</div>

> [@tbennett.tdc](#):
>
> but it is not the answer to my question

I think you are confused.

You should study my recommendation closer, and study the functionality of the EasyChart's `tagPens` property. Learn how window parameterization works, and how to use property bindings in components to receive window parameters from root container properties.

---

<div class="post-metadata">

**Author:** ![robertm](https://avatars.discourse-cdn.com/v4/letter/r/ea5d25/32.png) [@robertm](https://forum.inductiveautomation.com/u/robertm)\
**Post date:** [July 30, 2025, 4:21pm UTC](https://forum.inductiveautomation.com/t/create-easy-chart-pen-tags-from-udt-in-template/109096/6 "2025-07-30T16:21:59Z")

</div>

And what we are trying to explain is that you do that with a template property that points to your base UDT path. Create internal custom properties on the template that defines whatever you need (pen tag paths, axis properties, etc) and use cell bindings on the easy chart data sets to point to those custom properties.

---

<div class="post-metadata">

**Author:** ![tbennett.tdc](https://avatars.discourse-cdn.com/v4/letter/t/54ee81/32.png) [@tbennett.tdc](https://forum.inductiveautomation.com/u/tbennett.tdc)\
**Post date:** [July 30, 2025, 4:29pm UTC](https://forum.inductiveautomation.com/t/create-easy-chart-pen-tags-from-udt-in-template/109096/7 "2025-07-30T16:29:50Z")

</div>

Yes, I am confused, but mostly because you keep talking about passing information to the template during an action. Please read my post a little closer. I did not say anything about a popup or any other action. I was able to implement what you said via an action like a popup, but I want to fill in the Tag Path of the EasyChart Tag History Pens through property bindings without an action like invoking a popup. The Tag History Pens are directly related to tags in my tag UDT and the rest of my template is filled in by accessing UDT tags and properties without any actions required to do so. Just want to do the same with these.

---

<div class="post-metadata">

**Author:** ![tbennett.tdc](https://avatars.discourse-cdn.com/v4/letter/t/54ee81/32.png) [@tbennett.tdc](https://forum.inductiveautomation.com/u/tbennett.tdc)\
**Post date:** [July 30, 2025, 4:37pm UTC](https://forum.inductiveautomation.com/t/create-easy-chart-pen-tags-from-udt-in-template/109096/8 "2025-07-30T16:37:26Z")

</div>

Yes. But how? I can choose properties and tags in my template using built-in browsers to find them. How do I do that only knowing the base UDT tag and any custom properties I've created? What is the relationship between the historical tags in the UDT tag and their tag path for the historical database provider? As @pturmel said, I'm confused, but just on this linkage.

---

<div class="post-metadata">

**Author:** ![robertm](https://avatars.discourse-cdn.com/v4/letter/r/ea5d25/32.png) [@robertm](https://forum.inductiveautomation.com/u/robertm)\
**Post date:** [July 30, 2025, 4:55pm UTC](https://forum.inductiveautomation.com/t/create-easy-chart-pen-tags-from-udt-in-template/109096/9 "2025-07-30T16:55:06Z")

</div>

Heres a template with a sparkline...same pricinple. The property analog\_path holds the tag path to the udt root. The sparkline uses an indirect to tag history. For an easy chart, youll use cell update bindings instead to update the pens.

 ![20250730_125208](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/6/d66fddd95b242a28332d71031398cbd178ab2d22.jpeg)  
 ![20250730_125137](https://us1.discourse-cdn.com/inductiveautomation/original/3X/9/a/9ab68c4d3aa882015f48abafddcc2f82fe4f7aa5.jpeg)

---

<div class="post-metadata">

**Author:** ![tbennett.tdc](https://avatars.discourse-cdn.com/v4/letter/t/54ee81/32.png) [@tbennett.tdc](https://forum.inductiveautomation.com/u/tbennett.tdc)\
**Post date:** [July 30, 2025, 5:34pm UTC](https://forum.inductiveautomation.com/t/create-easy-chart-pen-tags-from-udt-in-template/109096/10 "2025-07-30T17:34:21Z")

</div>

While this doesn't get the Tag Path directly from the underlying template UDT, it does solve my problem for the most part.

I was able to create 2 Template Parameters (Strings) that hold the Tag Path of the 2 pens in my template Easy Chart. The only other Template Parameter I have is the TagInstance, which is the binding to the UDT tag for the template. These 2 new Template Properties are Strings so I have to figure out what the Tag Paths are and enter them here, but I wish there were a way to browse for History Tag Paths like there is for tags and properties.

Thanks for the understanding and help!

---

<div class="post-metadata">

**Author:** ![robertm](https://avatars.discourse-cdn.com/v4/letter/r/ea5d25/32.png) [@robertm](https://forum.inductiveautomation.com/u/robertm)\
**Post date:** [July 30, 2025, 5:39pm UTC](https://forum.inductiveautomation.com/t/create-easy-chart-pen-tags-from-udt-in-template/109096/11 "2025-07-30T17:39:17Z")

</div>

No problem. As noted in the other thread, you really should not pass udt tags to popups or templates, even though Ignition made it easy to do so. Should always pass a tag path string instead, and form your bindings with indirects or properties within the popup or template.

---

<div class="post-metadata">

**Author:** ![tbennett.tdc](https://avatars.discourse-cdn.com/v4/letter/t/54ee81/32.png) [@tbennett.tdc](https://forum.inductiveautomation.com/u/tbennett.tdc)\
**Post date:** [July 30, 2025, 5:46pm UTC](https://forum.inductiveautomation.com/t/create-easy-chart-pen-tags-from-udt-in-template/109096/12 "2025-07-30T17:46:18Z")

</div>

I saw that but don't understand enough about why to comment. It does make me curious enough to wonder why that's not recommended, but passing a dataset is a common recommendation. What makes a UDT different than other tag types? If it's not too much of a detailed explanation, maybe you could explain?

---

<div class="post-metadata">

**Author:** ![ryan.white](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ryan.white/32/73193_2.png) [@ryan.white](https://forum.inductiveautomation.com/u/ryan.white)\
**Post date:** [July 30, 2025, 5:57pm UTC](https://forum.inductiveautomation.com/t/create-easy-chart-pen-tags-from-udt-in-template/109096/13 "2025-07-30T17:57:34Z")

</div>

If you pass a UDT, Ignition will subscribe(might not be the right word) to EVERY tag in the udt structure, instead of pulling just the ones used in a display component. This will crush performance with large UDTs being used across multiple template instances at once (imagine 100 tags x however many template instances open at once instead of 3 tags x however many active template instances)

---

<div class="post-metadata">

**Author:** ![lrose](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/lrose/32/62724_2.png) [@lrose](https://forum.inductiveautomation.com/u/lrose)\
**Post date:** [July 30, 2025, 6:00pm UTC](https://forum.inductiveautomation.com/t/create-easy-chart-pen-tags-from-udt-in-template/109096/14 "2025-07-30T18:00:23Z")

</div>

> [@tbennett.tdc](#):
>
> What makes a UDT different than other tag types?

Mainly, a UDT isn't a tag, it's a type. And that can be a performance killer if you have large UDT's or you have many bindings to smaller UDT's.

Here is an applicable topic:

> [@Template using UDT param: Can you access UDT tag metadata?](https://forum.inductiveautomation.com/t/template-using-udt-param-can-you-access-udt-tag-metadata/10179):
>
> Hi all, I’m new to Ignition and have tried searching for this already with no luck. I have a template with a UDT as a parameter that contains some OPC tags. Can I access the metadata (e.g. Eng Units / Min/Max range, etc.) of this UDT parameter’s tags from inside the template? e.g. something like (which doesn’t work) {Tank Template.Tank::Temperature.PV.EngHigh} Where: Tank Template is the template Tank is the UDT parameter Temperature.PV is an OPC tag within the UDT EngHigh is the metadata…

---

<div class="post-metadata">

**Author:** ![tbennett.tdc](https://avatars.discourse-cdn.com/v4/letter/t/54ee81/32.png) [@tbennett.tdc](https://forum.inductiveautomation.com/u/tbennett.tdc)\
**Post date:** [July 30, 2025, 6:10pm UTC](https://forum.inductiveautomation.com/t/create-easy-chart-pen-tags-from-udt-in-template/109096/15 "2025-07-30T18:10:50Z")

</div>

I didn't say a UDT was a tag, I said it was a Tag Type. Thanks for the reply.

---

<div class="post-metadata">

**Author:** ![tbennett.tdc](https://avatars.discourse-cdn.com/v4/letter/t/54ee81/32.png) [@tbennett.tdc](https://forum.inductiveautomation.com/u/tbennett.tdc)\
**Post date:** [July 30, 2025, 6:13pm UTC](https://forum.inductiveautomation.com/t/create-easy-chart-pen-tags-from-udt-in-template/109096/16 "2025-07-30T18:13:03Z")

</div>

Thanks. Totally makes sense. My UDTs and Templates match 100% and all tags within the UDT are used by the template. I don't think this is a big killer of performance then, but maybe I'm wrong if there is more to it than that.

---

<div class="post-metadata">

**Author:** ![nminchin](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/nminchin/32/6911_2.png) [@nminchin](https://forum.inductiveautomation.com/u/nminchin)\
**Post date:** [July 31, 2025, 12:20am UTC](https://forum.inductiveautomation.com/t/create-easy-chart-pen-tags-from-udt-in-template/109096/17 "2025-07-31T00:20:26Z")

</div>

They also limit your usage of templates that use them. e.g. you can't pass UdtType parameters via script which is extremely limiting, you can't use them in template repeaters, etc.

If you want to design for flexibility and scalability, you **shouldn't** use them