> [@Anant\_Upadhyayula](#):
>
> I hate to create a separate udt based on PLC. but if that is the only viable route then I will do it.

Consider not including the tanks in the the device's overview UDT. Just use a folder with separate single "core" and multiple "tank" UDT instances.

~~You **cannot** make a UDT with a variable number of members, of any kind.~~

 

Also: You asked a form of this question over here:

> [@Dynamic udt instances](https://forum.inductiveautomation.com/t/dynamic-udt-instances/92767/4):
>
> I meant that you cannot have such a dynamic UDT structure at all. Just use a regular tag folder where you are currently trying to use a UDT.

~~Asking in a new topic won't change that answer.~~

---