> [@Koussaila\_Fekroune](#):
>
> where can I put my script

That old script is overdue for a refactor:

```python
# Written for the propertyChange event handler of an alarm status table
# The component running event only fires once when its component is first initialized
# It won't fire in the designer unless preview mode is on prior to opening the window
if event.propertyName == 'componentRunning':
		
	# Returns the first nested component of a given class
	# container = The object containing nested components to be recursively searched
	# className = the __name__ of the class given as a string
	def findComponentOfClass(container, className):
		for component in container.components:
			if component. __class__. __name__ == className:
				return component
			else:
				foundComponent = findComponentOfClass(component, className)
				if foundComponent:
					return foundComponent
	
	# Recursively find the inner table
	innerTable = findComponentOfClass(event.source, 'AlarmStatusTable$1')
	
	# Iterate through the table columns and conditionally change the header values in some way
	columnModel = innerTable.columnModel
	for column in xrange(innerTable.columnCount):
		tableColumn = columnModel.getColumn(column)
		if tableColumn.headerValue == 'Label':
			tableColumn.headerValue = 'Custom Alarm Name'
			
	# Repaint the table header
	innerTable.tableHeader.repaint()

```

This script was written for the `propertyChange` event handler of the Alarm Status table itself. Simply _ **right click on the alarm status table** _ in the designer. Then, _ **click on "Scripting"** _ in the popup that appears, and place the script in the propertyChange event handler: