# Data Acquisition

**URL:** <https://forum.inductiveautomation.com/t/data-acquisition/23763>\
**Category:** Ignition\
**Created:** [April 1, 2019, 7:46pm UTC](https://forum.inductiveautomation.com/t/data-acquisition/23763 "2019-04-01T19:46:54Z")\
**Posts on this page:** 11\
**Page:** 1

<div class="post-metadata">

**Author:** ![carolineuchoa.estuda](https://avatars.discourse-cdn.com/v4/letter/c/ba8739/32.png) [@carolineuchoa.estuda](https://forum.inductiveautomation.com/u/carolineuchoa.estuda)\
**Post date:** [April 1, 2019, 7:46pm UTC](https://forum.inductiveautomation.com/t/data-acquisition/23763/1 "2019-04-01T19:46:54Z")

</div>

Hello,

Is it possible that a frequency acquisition is less than 1Hz?  
I wanted to display this table below with more time intervals between seconds.

Thanks in advance!

![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/e/ede685e2e60804dd127d0fe61230a1cdbc6f6e3c.png)

---

<div class="post-metadata">

**Author:** ![MMaynard](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/mmaynard/32/3366_2.png) [@MMaynard](https://forum.inductiveautomation.com/u/MMaynard)\
**Post date:** [April 1, 2019, 8:17pm UTC](https://forum.inductiveautomation.com/t/data-acquisition/23763/2 "2019-04-01T20:17:48Z")

</div>

Change the formatting on the column to display the milliseconds.

---

<div class="post-metadata">

**Author:** ![carolineuchoa.estuda](https://avatars.discourse-cdn.com/v4/letter/c/ba8739/32.png) [@carolineuchoa.estuda](https://forum.inductiveautomation.com/u/carolineuchoa.estuda)\
**Post date:** [April 4, 2019, 5:07pm UTC](https://forum.inductiveautomation.com/t/data-acquisition/23763/3 "2019-04-04T17:07:34Z")

</div>

Actually I needed the sample size to be an interval of 250ms between records on the table

---

<div class="post-metadata">

**Author:** ![grietveld](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/grietveld/32/6984_2.png) [@grietveld](https://forum.inductiveautomation.com/u/grietveld)\
**Post date:** [April 4, 2019, 5:59pm UTC](https://forum.inductiveautomation.com/t/data-acquisition/23763/4 "2019-04-04T17:59:37Z")

</div>

You will probably have to adjust the timestamp formatting to include milliseconds. The next thing to check is to make sure that your datasource has the ability to capture and save at that rate. If you had data at 4 samples/second, I would expect to see 4 records with the same timestamp as formatted above.

---

<div class="post-metadata">

**Author:** ![carolineuchoa.estuda](https://avatars.discourse-cdn.com/v4/letter/c/ba8739/32.png) [@carolineuchoa.estuda](https://forum.inductiveautomation.com/u/carolineuchoa.estuda)\
**Post date:** [April 4, 2019, 6:36pm UTC](https://forum.inductiveautomation.com/t/data-acquisition/23763/5 "2019-04-04T18:36:07Z")

</div>

These images below are my current configuration of the table, sorry if that is a stupid question, but I don’t know how to make the sample size smaller than 1 second (as it just has 3 options: sec, min, hours). I know the datasource can capture and save at that rate, but I don’t know how to display it at the table.

Thanks

![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/1/199e5263c9d3238b599f02b450ceaf9fb280e8f9.png)

![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/a/a233e92c49a765e0ff55c018dc19800c055fea0d.png)

---

<div class="post-metadata">

**Author:** ![MMaynard](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/mmaynard/32/3366_2.png) [@MMaynard](https://forum.inductiveautomation.com/u/MMaynard)\
**Post date:** [April 4, 2019, 7:22pm UTC](https://forum.inductiveautomation.com/t/data-acquisition/23763/6 "2019-04-04T19:22:07Z")

</div>

You will have to first create an historical scan class set to 250ms  
Then set whatever trend tags you want that resolution at to use that scan class.  
Then you right click the table, go to Customize and set the format for the timestamp column to include the milliseconds.  
From the screenshots it looks like you have the historical scan class set to 1 second currently.

---

<div class="post-metadata">

**Author:** ![carolineuchoa.estuda](https://avatars.discourse-cdn.com/v4/letter/c/ba8739/32.png) [@carolineuchoa.estuda](https://forum.inductiveautomation.com/u/carolineuchoa.estuda)\
**Post date:** [April 4, 2019, 7:26pm UTC](https://forum.inductiveautomation.com/t/data-acquisition/23763/7 "2019-04-04T19:26:14Z")

</div>

Actually, the scan class was already set to 250ms

![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c24a0e0d5ecee0a5fa7a5266adfbef56a9c17a23.png)

---

<div class="post-metadata">

**Author:** ![MMaynard](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/mmaynard/32/3366_2.png) [@MMaynard](https://forum.inductiveautomation.com/u/MMaynard)\
**Post date:** [April 4, 2019, 7:41pm UTC](https://forum.inductiveautomation.com/t/data-acquisition/23763/8 "2019-04-04T19:41:22Z")

</div>

Then right click the table, customize, change the column format to include the milliseconds.  
Also change your query settings to Sample Size - Natural

---

<div class="post-metadata">

**Author:** ![MMaynard](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/mmaynard/32/3366_2.png) [@MMaynard](https://forum.inductiveautomation.com/u/MMaynard)\
**Post date:** [April 4, 2019, 7:50pm UTC](https://forum.inductiveautomation.com/t/data-acquisition/23763/9 "2019-04-04T19:50:45Z")

</div>

![MilliFormat](https://us1.discourse-cdn.com/inductiveautomation/original/2X/9/94bec670f339ea16a52a017e083cf536387c03db.png)

---

<div class="post-metadata">

**Author:** ![carolineuchoa.estuda](https://avatars.discourse-cdn.com/v4/letter/c/ba8739/32.png) [@carolineuchoa.estuda](https://forum.inductiveautomation.com/u/carolineuchoa.estuda)\
**Post date:** [April 4, 2019, 7:53pm UTC](https://forum.inductiveautomation.com/t/data-acquisition/23763/10 "2019-04-04T19:53:18Z")

</div>

It is now at 250ms rate! Thanks! But the value are constantly going to a bad quality value. Does that mean that the rate of my datasource is higher than 250ms?

![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/a/ae5ea60d1c53bba8808d8871e2a40dd00713a39d.png)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [April 4, 2019, 8:00pm UTC](https://forum.inductiveautomation.com/t/data-acquisition/23763/11 "2019-04-04T20:00:42Z")

</div>

> [@carolineuchoa.estuda](#):
>
> It is now at 250ms rate!

But they aren't displaying milliseconds -- you used a lower case 's', which gets you the seconds again.

> [@carolineuchoa.estuda](#):
>
> constantly going to a bad quality value

Yep, your PLC driver is having trouble with that pace.