# Data refreshing problem in ignition 8.1 with freyrSCADA as DNP3 simulator

**URL:** <https://forum.inductiveautomation.com/t/data-refreshing-problem-in-ignition-8-1-with-freyrscada-as-dnp3-simulator/109988>\
**Category:** Ignition\
**Tags:** ignition81\
**Created:** [August 20, 2025, 2:30pm UTC](https://forum.inductiveautomation.com/t/data-refreshing-problem-in-ignition-8-1-with-freyrscada-as-dnp3-simulator/109988 "2025-08-20T14:30:04Z")\
**Posts on this page:** 14\
**Page:** 1

<div class="post-metadata">

**Author:** ![Ahmed\_badawi1](https://avatars.discourse-cdn.com/v4/letter/a/58f4c7/32.png) [@Ahmed\_badawi1](https://forum.inductiveautomation.com/u/Ahmed_badawi1)\
**Post date:** [August 20, 2025, 2:30pm UTC](https://forum.inductiveautomation.com/t/data-refreshing-problem-in-ignition-8-1-with-freyrscada-as-dnp3-simulator/109988/1 "2025-08-20T14:30:04Z")

</div>

i have my Freyr SCADA DNP3 simulator, I wanted to connect it with ignition as DNP3 outstation and connection is successful, but I have a problem, tags values are only sent at the beginning of the connection and then it’s not updated even if it’s changed from outstation

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/9/3/93187b86ff16e9e70ff619e76864bbff7521bdc3.png)

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/6/c61a19467daea1160b719aa8b682d43f78eba509.png)

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/4/3/43cb8e109fb1bb8959a1470d15d67d1a9dbf6edb.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [August 20, 2025, 2:38pm UTC](https://forum.inductiveautomation.com/t/data-refreshing-problem-in-ignition-8-1-with-freyrscada-as-dnp3-simulator/109988/2 "2025-08-20T14:38:08Z")

</div>

Get a Wireshark capture and see if the simulated device is sending any events or value changes on subsequent integrity polls.

---

<div class="post-metadata">

**Author:** ![andrew.budaiev](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/andrew.budaiev/32/72921_2.png) [@andrew.budaiev](https://forum.inductiveautomation.com/u/andrew.budaiev)\
**Post date:** [August 21, 2025, 12:07am UTC](https://forum.inductiveautomation.com/t/data-refreshing-problem-in-ignition-8-1-with-freyrscada-as-dnp3-simulator/109988/3 "2025-08-21T00:07:34Z")

</div>

> [@Ahmed\_badawi1](#):
>
> tags values are only sent at the beginning of the connection and then it’s not updated even if it’s changed from outstation

Will it update if you restart the tag? Also, how is your tag group set up? I think if you have the rate set to 0 ms, the tag group will not execute.

---

<div class="post-metadata">

**Author:** ![Ahmed\_badawi1](https://avatars.discourse-cdn.com/v4/letter/a/58f4c7/32.png) [@Ahmed\_badawi1](https://forum.inductiveautomation.com/u/Ahmed_badawi1)\
**Post date:** [August 21, 2025, 11:13am UTC](https://forum.inductiveautomation.com/t/data-refreshing-problem-in-ignition-8-1-with-freyrscada-as-dnp3-simulator/109988/4 "2025-08-21T11:13:10Z")

</div>

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/8/781f98110e75fd2a53d2518cef035ef956c4984b.png)

i think it’s sending properly like in snip above!

---

<div class="post-metadata">

**Author:** ![Ahmed\_badawi1](https://avatars.discourse-cdn.com/v4/letter/a/58f4c7/32.png) [@Ahmed\_badawi1](https://forum.inductiveautomation.com/u/Ahmed_badawi1)\
**Post date:** [August 21, 2025, 11:14am UTC](https://forum.inductiveautomation.com/t/data-refreshing-problem-in-ignition-8-1-with-freyrscada-as-dnp3-simulator/109988/5 "2025-08-21T11:14:26Z")

</div>

I’m using default tag group!, restarting doesn’t do anything!

---

<div class="post-metadata">

**Author:** ![Ahmed\_badawi1](https://avatars.discourse-cdn.com/v4/letter/a/58f4c7/32.png) [@Ahmed\_badawi1](https://forum.inductiveautomation.com/u/Ahmed_badawi1)\
**Post date:** [August 21, 2025, 11:26am UTC](https://forum.inductiveautomation.com/t/data-refreshing-problem-in-ignition-8-1-with-freyrscada-as-dnp3-simulator/109988/6 "2025-08-21T11:26:40Z")

</div>

Update: writing to dnp3 outstation sim is successful !, it’s updating in sim but it’s not updating in ignition and tag retain its old value!

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/a/8/a8df194da05dc2d8d13be80117350cb12c2db999.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [August 21, 2025, 11:46am UTC](https://forum.inductiveautomation.com/t/data-refreshing-problem-in-ignition-8-1-with-freyrscada-as-dnp3-simulator/109988/7 "2025-08-21T11:46:24Z")

</div>

Share the pcap file. That screenshot doesn’t look normal.

---

<div class="post-metadata">

**Author:** ![Ahmed\_badawi1](https://avatars.discourse-cdn.com/v4/letter/a/58f4c7/32.png) [@Ahmed\_badawi1](https://forum.inductiveautomation.com/u/Ahmed_badawi1)\
**Post date:** [August 21, 2025, 12:23pm UTC](https://forum.inductiveautomation.com/t/data-refreshing-problem-in-ignition-8-1-with-freyrscada-as-dnp3-simulator/109988/8 "2025-08-21T12:23:56Z")

</div>

[DNP3\_pcap.zip](https://forum.inductiveautomation.com/uploads/short-url/uf2feqsboAYXA9WlcagAxluaL5g.zip) (5.1 MB)

i hope it’s working, this my first time with wireshark

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [August 21, 2025, 12:28pm UTC](https://forum.inductiveautomation.com/t/data-refreshing-problem-in-ignition-8-1-with-freyrscada-as-dnp3-simulator/109988/9 "2025-08-21T12:28:02Z")

</div>

In your Ignition DNP3 device config, try disabling "auto time sync", and also set the "unsolicited event classes" field to empty.

---

<div class="post-metadata">

**Author:** ![Ahmed\_badawi1](https://avatars.discourse-cdn.com/v4/letter/a/58f4c7/32.png) [@Ahmed\_badawi1](https://forum.inductiveautomation.com/u/Ahmed_badawi1)\
**Post date:** [August 21, 2025, 2:09pm UTC](https://forum.inductiveautomation.com/t/data-refreshing-problem-in-ignition-8-1-with-freyrscada-as-dnp3-simulator/109988/10 "2025-08-21T14:09:12Z")

</div>

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/9/5/95d6491002e43ea7561711046aeba8cf3a5909c8.png)

still the same exactly, i didn’t find a field like “auto time sync“ in ignition drive conf

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [August 21, 2025, 2:10pm UTC](https://forum.inductiveautomation.com/t/data-refreshing-problem-in-ignition-8-1-with-freyrscada-as-dnp3-simulator/109988/11 "2025-08-21T14:10:15Z")

</div>

Scroll down and look for a checkbox, it's in the Advanced category. If you don't have it then you need to upgrade.

---

<div class="post-metadata">

**Author:** ![Ahmed\_badawi1](https://avatars.discourse-cdn.com/v4/letter/a/58f4c7/32.png) [@Ahmed\_badawi1](https://forum.inductiveautomation.com/u/Ahmed_badawi1)\
**Post date:** [August 21, 2025, 2:13pm UTC](https://forum.inductiveautomation.com/t/data-refreshing-problem-in-ignition-8-1-with-freyrscada-as-dnp3-simulator/109988/12 "2025-08-21T14:13:31Z")

</div>

it’s added in version 8.1.39, i using 8.1.38

---

<div class="post-metadata">

**Author:** ![Ahmed\_badawi1](https://avatars.discourse-cdn.com/v4/letter/a/58f4c7/32.png) [@Ahmed\_badawi1](https://forum.inductiveautomation.com/u/Ahmed_badawi1)\
**Post date:** [August 21, 2025, 3:15pm UTC](https://forum.inductiveautomation.com/t/data-refreshing-problem-in-ignition-8-1-with-freyrscada-as-dnp3-simulator/109988/13 "2025-08-21T15:15:53Z")

</div>

wow, i upgraded to v8.1.49 and disabled it and it worked!

thanks

i just curious to know how you found it from wireshark file?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [August 21, 2025, 3:21pm UTC](https://forum.inductiveautomation.com/t/data-refreshing-problem-in-ignition-8-1-with-freyrscada-as-dnp3-simulator/109988/14 "2025-08-21T15:21:03Z")

</div>

Your simulator is setting the NEEDS\_TIME bit but doesn't seem to support either of the commands being used to try to set its time. Your capture is just full of attempts to sync the time, which has to be done before the rest of comms start.