# Data synchronization & storage problem

**URL:** <https://forum.inductiveautomation.com/t/data-synchronization-storage-problem/103572>\
**Category:** Ignition\
**Tags:** ignition81\
**Created:** [March 12, 2025, 1:28pm UTC](https://forum.inductiveautomation.com/t/data-synchronization-storage-problem/103572 "2025-03-12T13:28:19Z")\
**Posts on this page:** 5\
**Page:** 1

<div class="post-metadata">

**Author:** ![Rodrigo\_Bernardes](https://avatars.discourse-cdn.com/v4/letter/r/9de0a6/32.png) [@Rodrigo\_Bernardes](https://forum.inductiveautomation.com/u/Rodrigo_Bernardes)\
**Post date:** [March 12, 2025, 1:28pm UTC](https://forum.inductiveautomation.com/t/data-synchronization-storage-problem/103572/1 "2025-03-12T13:28:19Z")

</div>

Hi,

I'm trying to synchronize data between a Central Gateway and an Edge Gateway. The idea is to have permanent data on the Central Gateway while the Edge will be limited to it´s capacity, which today is being about 10 days.

The history data is arriving on the Central Gateway but the problem is it´s not storing beyond the available data on the Edge. It´s being a mirror of the Edge history.

On the central gateway I configured a History Tag Provider like bellow

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/8/6/861024c1cfbb1ecb76dae6b7f3c728e957b2f516.png)

but it´s showing a faulted status, even considering that I can see the history on a PowerChart. But as I said, limited to the amount of data in the edge gateway .

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/9/4/94fd5362dfa2372a5dc694320be27ee8a8da70f4.png)

---

<div class="post-metadata">

**Author:** ![pascal.fragnoud](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pascal.fragnoud/32/24728_2.png) [@pascal.fragnoud](https://forum.inductiveautomation.com/u/pascal.fragnoud)\
**Post date:** [March 12, 2025, 1:48pm UTC](https://forum.inductiveautomation.com/t/data-synchronization-storage-problem/103572/2 "2025-03-12T13:48:32Z")

</div>

You should have the historian on the central gateway, and the edge node connecting to it remotely.  
Have a tag history splitter on the edge to send data to both the remote historian and a local historian

---

<div class="post-metadata">

**Author:** ![Rodrigo\_Bernardes](https://avatars.discourse-cdn.com/v4/letter/r/9de0a6/32.png) [@Rodrigo\_Bernardes](https://forum.inductiveautomation.com/u/Rodrigo_Bernardes)\
**Post date:** [March 17, 2025, 5:04pm UTC](https://forum.inductiveautomation.com/t/data-synchronization-storage-problem/103572/3 "2025-03-17T17:04:33Z")

</div>

Hi,

I have had some progress but still a problem. 😒  
Now the data is going from Edge to the database in Central Gateway 🙌, but when I try to plot it in powerchart it shows only a line.

It seems like it´s showing only the last value, the line keeps changing it´s position.

Is it really possible to show data from databases on powerchart?

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/9/79ce4411b0fcce2762425dfe35d176453d1c7647.png)

Obs.: You said about a tag\_history\_splitter but I didn´t find this option on Edge. I'm doing it on Data Sync / Settings, where there´s onle way to put one "Remote History Provider Name".

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [March 17, 2025, 5:43pm UTC](https://forum.inductiveautomation.com/t/data-synchronization-storage-problem/103572/4 "2025-03-17T17:43:51Z")

</div>

It sounds like your configuration is scrambled in non-obvious ways. You should open a support ticket so IA can look over your shoulder.

---

<div class="post-metadata">

**Author:** ![Rodrigo\_Bernardes](https://avatars.discourse-cdn.com/v4/letter/r/9de0a6/32.png) [@Rodrigo\_Bernardes](https://forum.inductiveautomation.com/u/Rodrigo_Bernardes)\
**Post date:** [May 16, 2025, 12:42pm UTC](https://forum.inductiveautomation.com/t/data-synchronization-storage-problem/103572/5 "2025-05-16T12:42:12Z")

</div>

Hi, sorry for the delay.  
There was no problem with the configuration and it worked the way it was in the end.  
I saw later that the straight line only appear in first time I was accessing (plotting) the data. I guess it was kind of a bug. Usually I just needed to update the browse tags and wait some seconds for it to be plotted correct. I don´t know how, but it´s not happening anymore. Maybe because at the begginnig there was a bunch of previous data on the edge to be sent to the central database.