# Datasource fault

**URL:** <https://forum.inductiveautomation.com/t/datasource-fault/2610>\
**Category:** Archived Topics\
**Created:** [February 7, 2011, 6:54pm UTC](https://forum.inductiveautomation.com/t/datasource-fault/2610 "2011-02-07T18:54:16Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![Jcam](https://avatars.discourse-cdn.com/v4/letter/j/a88e57/32.png) [@Jcam](https://forum.inductiveautomation.com/u/Jcam)\
**Post date:** [February 7, 2011, 6:54pm UTC](https://forum.inductiveautomation.com/t/datasource-fault/2610/1 "2011-02-07T18:54:16Z")

</div>

When too many clients log on we get a datasource fault. What can we do to fix this?

This is what the datasource is currently running, a lot of times the Throughput is over 100 queries/sec

Total Queries 3,012,988  
Query Duration  
(Min / Avg / Max) 0.00 / 0.00 / 3.39  
Throughput 93.22 queries/sec

---

<div class="post-metadata">

**Author:** ![Travis.Cox](https://avatars.discourse-cdn.com/v4/letter/t/b9bd4f/32.png) [@Travis.Cox](https://forum.inductiveautomation.com/u/Travis.Cox)\
**Post date:** [February 7, 2011, 9:40pm UTC](https://forum.inductiveautomation.com/t/datasource-fault/2610/2 "2011-02-07T21:40:43Z")

</div>

It looks like your connection is getting overwhelmed. Two things you can do:

1. Try to consolidate queries

2. Increase the Max Active property for the DB connection in Ignition Gateway Configuration. It is an advanced setting on the connection edit screen.