# DB needed for Siemens addressing?

**URL:** <https://forum.inductiveautomation.com/t/db-needed-for-siemens-addressing/67801>\
**Category:** Ignition\
**Tags:** ignition81, perspective\
**Created:** [December 19, 2022, 7:20pm UTC](https://forum.inductiveautomation.com/t/db-needed-for-siemens-addressing/67801 "2022-12-19T19:20:25Z")\
**Posts on this page:** 8\
**Page:** 1

<div class="post-metadata">

**Author:** ![mjohnson0238](https://avatars.discourse-cdn.com/v4/letter/m/4bbf92/32.png) [@mjohnson0238](https://forum.inductiveautomation.com/u/mjohnson0238)\
**Post date:** [December 19, 2022, 7:20pm UTC](https://forum.inductiveautomation.com/t/db-needed-for-siemens-addressing/67801/1 "2022-12-19T19:20:25Z")

</div>

Is a DB needed for the addressing to work? I need to read an Input ,I1016.4, but it doesnt exist in a DB,

Thanks

---

<div class="post-metadata">

**Author:** ![craigb](https://avatars.discourse-cdn.com/v4/letter/c/9f8e36/32.png) [@craigb](https://forum.inductiveautomation.com/u/craigb)\
**Post date:** [December 19, 2022, 7:29pm UTC](https://forum.inductiveautomation.com/t/db-needed-for-siemens-addressing/67801/2 "2022-12-19T19:29:09Z")

</div>

Inputs, Outputs, Markers etc you should be able to read directly.

Try..

IX1016.4

[https://docs.inductiveautomation.com/display/DOC80/Siemens](https://docs.inductiveautomation.com/display/DOC80/Siemens)

---

<div class="post-metadata">

**Author:** ![mjohnson0238](https://avatars.discourse-cdn.com/v4/letter/m/4bbf92/32.png) [@mjohnson0238](https://forum.inductiveautomation.com/u/mjohnson0238)\
**Post date:** [December 19, 2022, 7:35pm UTC](https://forum.inductiveautomation.com/t/db-needed-for-siemens-addressing/67801/3 "2022-12-19T19:35:06Z")

</div>

I have the tag configured like this returning a BAD:  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/9/f95bb03b7ca050ed95056f888a2dc90a8bed8fe7.png)

---

<div class="post-metadata">

**Author:** ![craigb](https://avatars.discourse-cdn.com/v4/letter/c/9f8e36/32.png) [@craigb](https://forum.inductiveautomation.com/u/craigb)\
**Post date:** [December 19, 2022, 7:37pm UTC](https://forum.inductiveautomation.com/t/db-needed-for-siemens-addressing/67801/4 "2022-12-19T19:37:50Z")

</div>

And you are able to read other areas (DB's etc) of the same PLC ?

---

<div class="post-metadata">

**Author:** ![mjohnson0238](https://avatars.discourse-cdn.com/v4/letter/m/4bbf92/32.png) [@mjohnson0238](https://forum.inductiveautomation.com/u/mjohnson0238)\
**Post date:** [December 19, 2022, 7:38pm UTC](https://forum.inductiveautomation.com/t/db-needed-for-siemens-addressing/67801/5 "2022-12-19T19:38:18Z")

</div>

Yes, sir

---

<div class="post-metadata">

**Author:** ![craigb](https://avatars.discourse-cdn.com/v4/letter/c/9f8e36/32.png) [@craigb](https://forum.inductiveautomation.com/u/craigb)\
**Post date:** [December 19, 2022, 7:43pm UTC](https://forum.inductiveautomation.com/t/db-needed-for-siemens-addressing/67801/6 "2022-12-19T19:43:54Z")

</div>

Unfortunately I use the Siemens OPC rather then Ignition OPC so have nothing to compare to.

What do you have for the permissions on the Inputs..?

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/6/f66b402a59521dccbd9d030654fa0f2cc4c5ba2a.png)

---

<div class="post-metadata">

**Author:** ![mjohnson0238](https://avatars.discourse-cdn.com/v4/letter/m/4bbf92/32.png) [@mjohnson0238](https://forum.inductiveautomation.com/u/mjohnson0238)\
**Post date:** [December 19, 2022, 7:57pm UTC](https://forum.inductiveautomation.com/t/db-needed-for-siemens-addressing/67801/7 "2022-12-19T19:57:00Z")

</div>

With you mentioning permissions and it being an OEM PLC, we may not have rights for the inputs. We also use the OPC for most of the tags we want to view, this just happens to be one thats not in the OPC server of the PLC.

Sorry to bother thanks

---

<div class="post-metadata">

**Author:** ![craigb](https://avatars.discourse-cdn.com/v4/letter/c/9f8e36/32.png) [@craigb](https://forum.inductiveautomation.com/u/craigb)\
**Post date:** [December 19, 2022, 8:31pm UTC](https://forum.inductiveautomation.com/t/db-needed-for-siemens-addressing/67801/8 "2022-12-19T20:31:37Z")

</div>

It could also mean that 'put/get' is not enabled, which it doesn't need to be if your other tags come from the Siemens OPC. Either way, without the PLC program there isn't much you can do.

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/d/dd5dcabf39fb03343768765e73b8ab30ec9f20b3.png)