# Deciphering overflow and underflow conditions coming from Analog inputs

**URL:** <https://forum.inductiveautomation.com/t/deciphering-overflow-and-underflow-conditions-coming-from-analog-inputs/77035>\
**Category:** Ignition\
**Tags:** vision\
**Created:** [July 27, 2023, 6:53pm UTC](https://forum.inductiveautomation.com/t/deciphering-overflow-and-underflow-conditions-coming-from-analog-inputs/77035 "2023-07-27T18:53:27Z")\
**Posts on this page:** 8\
**Page:** 1

<div class="post-metadata">

**Author:** ![Kevin\_Zornes](https://avatars.discourse-cdn.com/v4/letter/k/ee59a6/32.png) [@Kevin\_Zornes](https://forum.inductiveautomation.com/u/Kevin_Zornes)\
**Post date:** [July 27, 2023, 6:53pm UTC](https://forum.inductiveautomation.com/t/deciphering-overflow-and-underflow-conditions-coming-from-analog-inputs/77035/1 "2023-07-27T18:53:27Z")

</div>

Is there any way to ignore underflow and overflow signals coming from a PLC. Seems that tags don,t know how to decipher this.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [July 27, 2023, 6:55pm UTC](https://forum.inductiveautomation.com/t/deciphering-overflow-and-underflow-conditions-coming-from-analog-inputs/77035/2 "2023-07-27T18:55:18Z")

</div>

Can you elaborate?

---

<div class="post-metadata">

**Author:** ![Kevin\_Zornes](https://avatars.discourse-cdn.com/v4/letter/k/ee59a6/32.png) [@Kevin\_Zornes](https://forum.inductiveautomation.com/u/Kevin_Zornes)\
**Post date:** [July 27, 2023, 7:28pm UTC](https://forum.inductiveautomation.com/t/deciphering-overflow-and-underflow-conditions-coming-from-analog-inputs/77035/3 "2023-07-27T19:28:34Z")

</div>

I am reading an input word from a Seimens S7-1200. When the field device is in active, below 4 ma underflow the input word goes negative. The tag displays a positive number outside of the engineering High limit set.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [July 27, 2023, 7:29pm UTC](https://forum.inductiveautomation.com/t/deciphering-overflow-and-underflow-conditions-coming-from-analog-inputs/77035/4 "2023-07-27T19:29:47Z")

</div>

What datatype is the Ignition tag set as and what is the address (OPC Item Path) you used?

---

<div class="post-metadata">

**Author:** ![Transistor](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/transistor/32/3380_2.png) [@Transistor](https://forum.inductiveautomation.com/u/Transistor)\
**Post date:** [July 27, 2023, 7:31pm UTC](https://forum.inductiveautomation.com/t/deciphering-overflow-and-underflow-conditions-coming-from-analog-inputs/77035/5 "2023-07-27T19:31:28Z")

</div>

> [@Kevin\_Zornes](#):
>
> When the field device is in active, below 4 ma underflow the input word goes negative. The tag displays a positive number outside of the engineering High limit set.

How can it be negative and postitive at the same time. Can you write the problem more clearly?

---

<div class="post-metadata">

**Author:** ![Kevin\_Zornes](https://avatars.discourse-cdn.com/v4/letter/k/ee59a6/32.png) [@Kevin\_Zornes](https://forum.inductiveautomation.com/u/Kevin_Zornes)\
**Post date:** [July 27, 2023, 7:33pm UTC](https://forum.inductiveautomation.com/t/deciphering-overflow-and-underflow-conditions-coming-from-analog-inputs/77035/6 "2023-07-27T19:33:54Z")

</div>

I have the data type set as float. In this specific case the item patch is set up as [Grinding PLC]IW96. as per instructions on connecting to a Seimens device.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [July 27, 2023, 7:37pm UTC](https://forum.inductiveautomation.com/t/deciphering-overflow-and-underflow-conditions-coming-from-analog-inputs/77035/7 "2023-07-27T19:37:50Z")

</div>

`IW96` is an _unsigned_ type. If you're expecting to see negative values you need a signed type. Try `II96`, and see the [address syntax reference here](https://docs.inductiveautomation.com/display/DOC81/Siemens).

Further, if you're actually expecting a floating point value, then neither of these types are correct.

---

<div class="post-metadata">

**Author:** ![Kevin\_Zornes](https://avatars.discourse-cdn.com/v4/letter/k/ee59a6/32.png) [@Kevin\_Zornes](https://forum.inductiveautomation.com/u/Kevin_Zornes)\
**Post date:** [July 27, 2023, 7:43pm UTC](https://forum.inductiveautomation.com/t/deciphering-overflow-and-underflow-conditions-coming-from-analog-inputs/77035/8 "2023-07-27T19:43:10Z")

</div>

That worked. I changed the tag to integer and OPC to II96. Thank you very much.