# Device connection is overloading like crazy

**URL:** <https://forum.inductiveautomation.com/t/device-connection-is-overloading-like-crazy/113500>\
**Category:** Ignition\
**Created:** [January 22, 2026, 10:35pm UTC](https://forum.inductiveautomation.com/t/device-connection-is-overloading-like-crazy/113500 "2026-01-22T22:35:32Z")\
**Posts on this page:** 1\
**Showing post:** 7

<div class="post-metadata">

**Author:** ![michael.flagler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.flagler/32/26272_2.png) [@michael.flagler](https://forum.inductiveautomation.com/u/michael.flagler)\
**Post date:** [January 23, 2026, 1:05am UTC](https://forum.inductiveautomation.com/t/device-connection-is-overloading-like-crazy/113500/7 "2026-01-23T01:05:59Z")

</div>

When you say theyr'e complex nested UDTs, how big (in bytes) is your base UDT? Are you reading all/most tags in these UDTs or just some? What do your tag groups look like? Are you doing direct on everything or using leased tags? I've found doing all direct is usually faster because it doesn't add extra load/processing of changing poll rates of tags, but that's just my opinion.

Have you tried testing Phil's driver to see if you get better results? It's a drop-in replacement for the Ignition driver.

> [@Automation Professionals' EtherNet/IP Communication Suite V2](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/198):
>
> Better bugfix for the duplicate FwdOpen reconnection bug. I have an L81 in my lab that doesn't appear to allow recycling connection triads as expected. frowning For Ignition v8.3: [v2.2.1.260091944](https://www.automation-pros.com/ignition/EthernetIP%20Class%201%20Communications-2.2.1.260091944-v83.modl)

---

_[View the full topic](https://forum.inductiveautomation.com/t/device-connection-is-overloading-like-crazy/113500)._