# Device connections AllenBradley

**URL:** <https://forum.inductiveautomation.com/t/device-connections-allenbradley/52735>\
**Category:** Ignition\
**Created:** [November 4, 2021, 5:35pm UTC](https://forum.inductiveautomation.com/t/device-connections-allenbradley/52735 "2021-11-04T17:35:12Z")\
**Posts on this page:** 1\
**Showing post:** 10

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [November 5, 2021, 11:48am UTC](https://forum.inductiveautomation.com/t/device-connections-allenbradley/52735/10 "2021-11-05T11:48:19Z")

</div>

You might also want to review this topic if you are reading much from AOIs:

> [@Cannot read some tags inside Rockwell AOI](https://forum.inductiveautomation.com/t/cannot-read-some-tags-inside-rockwell-aoi/38393):
>
> I am trying to see tags inside an AOI. I went back to basics and dragged and dropped the tags from the OPC browser into the Tags Folder, but the quality is bad and there is a red x next to them. What is more confusing is that some are working and some are not. I cannot see any similarities between the few that aren’t working. Data type, In and Out types are working and not working. I can create a new UDT as an In/Out but this seems cumbersome. In this case, I would need to create tags only fo…

Also, avoid reading alias tags. (I recommend avoiding aliases, period.)

---

_[View the full topic](https://forum.inductiveautomation.com/t/device-connections-allenbradley/52735)._