Hello all,

I just wanted to bring this back to life real quick because I have some questions regarding the newer L80 processors. I currently have 8,963 tags and I am using the Gb port on the front of the PLC solely for my Ignition server. My switch says I am hovering right around 2-2.1Mbps on the port for the PLC. My load factor is at 95%. Why is this so? Why am I not able to use at least half the bandwidth available to me? If this sounds like I don’t know what I am talking about, its because I don’t. That is why I am here. My IO comms on the L83E is only around 4-4.6% actual vs theoretical. The only thing I see is the MSG Class 3 at 97%. My CPU is idle 74% of the time… Is there anyway to allow more time for comms or to adjust this in any way to get more out of the PLC gigabit port?

---