# Device Overload

**URL:** <https://forum.inductiveautomation.com/t/device-overload/85055>\
**Category:** Ignition\
**Created:** [January 31, 2024, 10:13pm UTC](https://forum.inductiveautomation.com/t/device-overload/85055 "2024-01-31T22:13:24Z")\
**Posts on this page:** 11\
**Page:** 1

<div class="post-metadata">

**Author:** ![Pat\_Cunningham](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pat_cunningham/32/57710_2.png) [@Pat\_Cunningham](https://forum.inductiveautomation.com/u/Pat_Cunningham)\
**Post date:** [January 31, 2024, 10:13pm UTC](https://forum.inductiveautomation.com/t/device-overload/85055/1 "2024-01-31T22:13:24Z")

</div>

I am trying to manage my device overload. I am currently at 45% and I have two questions.

1. I tried putting all of my tags in a leased group and setting the rate to 60000. I do not have a session open but I am still at 45%. What would be causing the 45% if I have no session open and all of my tags are leased.

2. I would like to identify all of the tags that are not used at all. I tried getting the latest version and using View Tag Diagnostics but that would require me to hit every single tag and if they are referred to indirectly it does not pick them up. Is there an easier way?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [January 31, 2024, 10:53pm UTC](https://forum.inductiveautomation.com/t/device-overload/85055/2 "2024-01-31T22:53:08Z")

</div>

Not enough information. Please provide:

- PLC Brand/mode/firmware

- Ignition Driver or OPC connection?

- Are leased tags mixed into the same PLC tags or address ranges as direct subscriptions? (They might have been optimized together, such that omitting the leased tags doesn't improve matters.)

- How many total subscribed items (shown on driver diagnostic page)?

---

<div class="post-metadata">

**Author:** ![Pat\_Cunningham](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pat_cunningham/32/57710_2.png) [@Pat\_Cunningham](https://forum.inductiveautomation.com/u/Pat_Cunningham)\
**Post date:** [February 1, 2024, 12:53pm UTC](https://forum.inductiveautomation.com/t/device-overload/85055/3 "2024-02-01T12:53:43Z")

</div>

Rockwell CompactLogix L33ER  
OPC UA  
No, currently every tag is part of a leased group

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/1/5/15e3e5102db56021a603fa55f0db8c5fea10c331.png)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [February 1, 2024, 1:23pm UTC](https://forum.inductiveautomation.com/t/device-overload/85055/4 "2024-02-01T13:23:00Z")

</div>

Looks like most of your tags are still in a 1000ms group.

---

<div class="post-metadata">

**Author:** ![Pat\_Cunningham](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pat_cunningham/32/57710_2.png) [@Pat\_Cunningham](https://forum.inductiveautomation.com/u/Pat_Cunningham)\
**Post date:** [February 1, 2024, 2:43pm UTC](https://forum.inductiveautomation.com/t/device-overload/85055/5 "2024-02-01T14:43:23Z")

</div>

The only group that is 1000s is the default group and there are no tags in it. I used the Tag Report Tool and there no tags in default and every other group is leased at 60000.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 1, 2024, 2:46pm UTC](https://forum.inductiveautomation.com/t/device-overload/85055/6 "2024-02-01T14:46:10Z")

</div>

What are the slow and fast rates of the leased group?

---

<div class="post-metadata">

**Author:** ![Pat\_Cunningham](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pat_cunningham/32/57710_2.png) [@Pat\_Cunningham](https://forum.inductiveautomation.com/u/Pat_Cunningham)\
**Post date:** [February 1, 2024, 4:07pm UTC](https://forum.inductiveautomation.com/t/device-overload/85055/7 "2024-02-01T16:07:41Z")

</div>

Fast 1000  
Slow 60000

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 1, 2024, 4:10pm UTC](https://forum.inductiveautomation.com/t/device-overload/85055/8 "2024-02-01T16:10:13Z")

</div>

Ok, well the obvious conclusion is that many of your tags are still being leased by _something_ and running at the fast rate.

Call support and let them take a look around.

---

<div class="post-metadata">

**Author:** ![Pat\_Cunningham](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pat_cunningham/32/57710_2.png) [@Pat\_Cunningham](https://forum.inductiveautomation.com/u/Pat_Cunningham)\
**Post date:** [February 1, 2024, 4:49pm UTC](https://forum.inductiveautomation.com/t/device-overload/85055/9 "2024-02-01T16:49:19Z")

</div>

I will. Do you have any suggestions on the second question?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 1, 2024, 4:54pm UTC](https://forum.inductiveautomation.com/t/device-overload/85055/10 "2024-02-01T16:54:07Z")

</div>

It might be something the [Tag Report Tool](https://docs.inductiveautomation.com/display/DOC81/Tag+Report+Tool) can help with, but I'm not familiar enough with it to be sure.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [February 1, 2024, 6:09pm UTC](https://forum.inductiveautomation.com/t/device-overload/85055/11 "2024-02-01T18:09:26Z")

</div>

The new tag reference tracking should work, but you **will** have to exercise the system to cover everything.