I have a customer with a SLC5/04 processor and the only option of getting data is from DH+. The other ports are already in use. I found this post below in another thread.

[quote]  
If connecting to a DH+ network the following options work:

```
- ControlLogix Gateway - this has many options but usually includes a Ethernet module(s) like ENBT, EN2T, etc. In addition to the Ethernet module they may also have DHRIO module(s) to bridge to DH+ networks or CNBT module(s) to bridge to ControlNet networks. This option can even bridge to other Ethernet networks. It is the fastest and most capable but comes with a higher price tag.

- Datalink Tech GW1000-ABEIP
- Equustek Solutions EQ7000 Eithernet to DH+ interface.

```

Refer to this forum post for more information about the last two options.  
viewtopic.php?f=55&t=7950&p=27532&hilit=DataLink#p27532[/quote]

I do not have the ControlLogix option, are the Datalink and Equustek the only two options that have been tested? This post was form 2012 so I am hoping there are more than two options to present to the customer.

Thanks in advance for any help.  
Knowles

---

<div class="post-metadata">

**Author:** ![AutomationNC](https://avatars.discourse-cdn.com/v4/letter/a/a587f6/32.png) [@AutomationNC](https://forum.inductiveautomation.com/u/AutomationNC)\
**Post date:** [August 13, 2015, 3:22pm UTC](https://forum.inductiveautomation.com/t/dh-slc5-04/10073/2 "2015-08-13T15:22:40Z")

</div>

I have used the DataLink GW 1000 with the latest version of Ignition with success. it is very easy to setup and works well.

---

<div class="post-metadata">

**Author:** ![JoeJansen](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/joejansen/32/5277_2.png) [@JoeJansen](https://forum.inductiveautomation.com/u/JoeJansen)\
**Post date:** [August 20, 2015, 8:14pm UTC](https://forum.inductiveautomation.com/t/dh-slc5-04/10073/3 "2015-08-20T20:14:22Z")

</div>

Also check this thread…

[https://inductiveautomation.com/forum/viewtopic.php?f=25&t=14293](https://inductiveautomation.com/forum/viewtopic.php?f=25&t=14293)