Just upgraded to Ignition 8.0.3 and noticed that Devices that are Disabled on the Gateway still show up in the OPC Browser and show live tag data. If I create a new Tag the tag will update even though the Device is Disabled in the Gateway settings. Is this normal?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [September 5, 2019, 8:38pm UTC](https://forum.inductiveautomation.com/t/disabled-device-on-the-gateway-still-shows-live-tag-values/28052/2 "2019-09-05T20:38:50Z")

</div>

What kind of device was it?

---

<div class="post-metadata">

**Author:** ![qversa](https://avatars.discourse-cdn.com/v4/letter/q/35a633/32.png) [@qversa](https://forum.inductiveautomation.com/u/qversa)\
**Post date:** [September 5, 2019, 9:03pm UTC](https://forum.inductiveautomation.com/t/disabled-device-on-the-gateway-still-shows-live-tag-values/28052/3 "2019-09-05T21:03:58Z")

</div>

ControlLogix using Allen-Bradley Logix Driver

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [September 5, 2019, 9:10pm UTC](https://forum.inductiveautomation.com/t/disabled-device-on-the-gateway-still-shows-live-tag-values/28052/4 "2019-09-05T21:10:20Z")

</div>

I’m not seeing this behavior on 8.0.3 or the latest development branch. Are you sure you actually disable the device?

---

<div class="post-metadata">

**Author:** ![qversa](https://avatars.discourse-cdn.com/v4/letter/q/35a633/32.png) [@qversa](https://forum.inductiveautomation.com/u/qversa)\
**Post date:** [September 5, 2019, 9:19pm UTC](https://forum.inductiveautomation.com/t/disabled-device-on-the-gateway-still-shows-live-tag-values/28052/5 "2019-09-05T21:19:00Z")

</div>

Yes, it’s Disabled at the Gateway. Just for fun I Enabled it, saved, then Disabled it and saved. I can still get live tag data. This Gateway was restored from another Gateway which is still up and running on the network. Is there some way the Device could be pointed to the OPC Server on the other Gateway? I actually have several devices that are doing this. I’ve never had this issue before.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [September 5, 2019, 9:23pm UTC](https://forum.inductiveautomation.com/t/disabled-device-on-the-gateway-still-shows-live-tag-values/28052/6 "2019-09-05T21:23:42Z")

</div>

Check your OPC UA connection, not any of the devices, and see if it’s pointed at localhost or some other IP address.

---

<div class="post-metadata">

**Author:** ![qversa](https://avatars.discourse-cdn.com/v4/letter/q/35a633/32.png) [@qversa](https://forum.inductiveautomation.com/u/qversa)\
**Post date:** [September 5, 2019, 9:35pm UTC](https://forum.inductiveautomation.com/t/disabled-device-on-the-gateway-still-shows-live-tag-values/28052/7 "2019-09-05T21:35:18Z")

</div>

OPC UA \> Server Settings \> Endpoint Addresses: ,

---

<div class="post-metadata">

**Author:** ![qversa](https://avatars.discourse-cdn.com/v4/letter/q/35a633/32.png) [@qversa](https://forum.inductiveautomation.com/u/qversa)\
**Post date:** [September 5, 2019, 9:36pm UTC](https://forum.inductiveautomation.com/t/disabled-device-on-the-gateway-still-shows-live-tag-values/28052/9 "2019-09-05T21:36:26Z")

</div>

hostname and localhost

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [September 5, 2019, 9:36pm UTC](https://forum.inductiveautomation.com/t/disabled-device-on-the-gateway-still-shows-live-tag-values/28052/10 "2019-09-05T21:36:29Z")

</div>

No, under OPC Client \> OPC Connections. Then click “More” \> “endpoint”.

If that’s not pointing to another server then you’ll probably need to call support and let them look around.

---

<div class="post-metadata">

**Author:** ![qversa](https://avatars.discourse-cdn.com/v4/letter/q/35a633/32.png) [@qversa](https://forum.inductiveautomation.com/u/qversa)\
**Post date:** [September 5, 2019, 9:39pm UTC](https://forum.inductiveautomation.com/t/disabled-device-on-the-gateway-still-shows-live-tag-values/28052/11 "2019-09-05T21:39:02Z")

</div>

Bingo, that was it. Thanks!