# DNP3 Driver - Tags updating but not adding history after switching to non-GVI address syntax

**URL:** <https://forum.inductiveautomation.com/t/dnp3-driver-tags-updating-but-not-adding-history-after-switching-to-non-gvi-address-syntax/101591>\
**Category:** Ignition\
**Tags:** ignition81\
**Created:** [January 30, 2025, 12:01am UTC](https://forum.inductiveautomation.com/t/dnp3-driver-tags-updating-but-not-adding-history-after-switching-to-non-gvi-address-syntax/101591 "2025-01-30T00:01:27Z")\
**Posts on this page:** 12\
**Page:** 1

<div class="post-metadata">

**Author:** ![tyler.bennett](https://avatars.discourse-cdn.com/v4/letter/t/f04885/32.png) [@tyler.bennett](https://forum.inductiveautomation.com/u/tyler.bennett)\
**Post date:** [January 30, 2025, 12:01am UTC](https://forum.inductiveautomation.com/t/dnp3-driver-tags-updating-but-not-adding-history-after-switching-to-non-gvi-address-syntax/101591/1 "2025-01-30T00:01:27Z")

</div>

While trying to convert DNP3 communications for an [SEL-735 (Schweitzer Power Quality and Revenue Meter)](https://selinc.com/products/735/) device from using [Explicit Reads (GVI syntax addressing)](https://www.docs.inductiveautomation.com/docs/8.1/ignition-modules/opc-ua/opc-ua-drivers/dnp3/dnp3-driver#explicit-reads) to either [Event Based Polling](https://www.docs.inductiveautomation.com/docs/8.1/ignition-modules/opc-ua/opc-ua-drivers/dnp3/dnp3-driver#event-based-polling) or [Event Based Unsolicited Messages](https://www.docs.inductiveautomation.com/docs/8.1/ignition-modules/opc-ua/opc-ua-drivers/dnp3/dnp3-driver#unsolicited-messaging) I have come across an issue where the tag value is updating frequently but nothing is being added to tag history.  
If I switch the tag **Value Source** from **OPC** to **Memory** and manually make changes then tag history is updated. If I switch the tag **OPC Item Path** to use a GVI syntax address then tag history is updated but when I switch the tag OPC Item Path to use the syntax required for Event Based Polling of Unsolicited Messaging then I see the tag value is getting updated but nothing is being added to tag History.  
I have reduced the testing down to a single test tag using the device connection to eliminate other factors.  
Ignition v8.1.45  
Device: SEL-735

I'm hoping the forum can offer some suggestions on next steps or point me at findings from others with similar issues.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [January 30, 2025, 12:05am UTC](https://forum.inductiveautomation.com/t/dnp3-driver-tags-updating-but-not-adding-history-after-switching-to-non-gvi-address-syntax/101591/2 "2025-01-30T00:05:23Z")

</div>

Maybe something to do with the timestamps?

Did you set up the necessary Tag Group options detailed here: [DNP3 Driver | Ignition User Manual](https://docs.inductiveautomation.com/docs/8.1/ignition-modules/opc-ua/opc-ua-drivers/dnp3/dnp3-driver#sequence-of-events)

Have you tried enabling Back-fill on the Tag Provider? [Tag Providers | Ignition User Manual](https://docs.inductiveautomation.com/docs/8.1/platform/tags/tag-providers#standard-tag-provider-1)

If you have both these things configured, add some logging to a tag change event script on that tag, log the full value, pay close attention to the timestamp.

---

<div class="post-metadata">

**Author:** ![tyler.bennett](https://avatars.discourse-cdn.com/v4/letter/t/f04885/32.png) [@tyler.bennett](https://forum.inductiveautomation.com/u/tyler.bennett)\
**Post date:** [January 30, 2025, 12:33am UTC](https://forum.inductiveautomation.com/t/dnp3-driver-tags-updating-but-not-adding-history-after-switching-to-non-gvi-address-syntax/101591/3 "2025-01-30T00:33:37Z")

</div>

I had already done two out of your three suggestions.

1. I already added logging to the tag **Value Changed** script.

```python
print tagPath, previousValue, currentValue, initialChange, missedEvents

```

The entries in the wrapper.log file don't reveal any issues.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/9/5934b42f3dbea91bdccb970b95886eacabc93dad.png)

1. A tag group is being used with Sampling Interval set to zero (0) and queue size set at a arbitrary large number. Is there anything else significant for the tag group settings? I find the terminology around "MonitoredItem" to be unclear in [the manual](https://www.docs.inductiveautomation.com/docs/8.1/ignition-modules/opc-ua/opc-ua-drivers/dnp3/dnp3-driver).  
**Tag Group:**  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/7/776b56f49062ca4994430cafcd47bcf6130815b6.png)  
**Tag Config:**  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/e/2e278b98864a5411a41ef386d67eb60b44fbcc43.png)
2. I had not previously tried enabling Back-fill on the Tag Provider. But on your suggestion tried it and it did not change the behavior. Reading the description I don't think I want to leave it on as I'd rather the tags get processed sequentially.  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/6/266c787a1edea153b1a0d07178ea4c39f67d8bdf.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [January 30, 2025, 12:37am UTC](https://forum.inductiveautomation.com/t/dnp3-driver-tags-updating-but-not-adding-history-after-switching-to-non-gvi-address-syntax/101591/4 "2025-01-30T00:37:39Z")

</div>

Your timestamps look wrong or in the past... I'm not sure the history system will store any data with a past timestamp unless backfill is enabled.

---

<div class="post-metadata">

**Author:** ![tyler.bennett](https://avatars.discourse-cdn.com/v4/letter/t/f04885/32.png) [@tyler.bennett](https://forum.inductiveautomation.com/u/tyler.bennett)\
**Post date:** [January 30, 2025, 12:46am UTC](https://forum.inductiveautomation.com/t/dnp3-driver-tags-updating-but-not-adding-history-after-switching-to-non-gvi-address-syntax/101591/5 "2025-01-30T00:46:39Z")

</div>

> [@Kevin.Herron](#):
>
> Your timestamps look wrong or in the past...

Ah, I see it now. I had been focused on the timestamps relative to each other.  
It appears the DNP connection is taking UTC timestamps from the device and recognizing them as Central time. Not sure how to correct that but you've given me an avenue to explore. Thanks!

---

<div class="post-metadata">

**Author:** ![ggross](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ggross/32/12668_2.png) [@ggross](https://forum.inductiveautomation.com/u/ggross)\
**Post date:** [January 30, 2025, 12:52am UTC](https://forum.inductiveautomation.com/t/dnp3-driver-tags-updating-but-not-adding-history-after-switching-to-non-gvi-address-syntax/101591/6 "2025-01-30T00:52:23Z")

</div>

For further troubleshooting, you can also enable `Context Logging` for a specific tag name that will increase logging for that specific tag and might give further insight into the decisions Ignition is making. This can be done by doing the following:

1. Navigate to `Status > Logs`
2. Click the gear to bring up the `Log Configuration` dialog
3. Click the `Context` tab
4. For `Key` enter: `tag`
5. For `Value` enter the tag name (not the path, just the name. For some reason we only support name which is a separate issue.)
6. For `Set Level` select: `TRACE`
7. Click `Add Level` button

This will enable TRACE logging for that specific tag name for all the important loggers related to tags including value changes and history logging.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [January 30, 2025, 12:56am UTC](https://forum.inductiveautomation.com/t/dnp3-driver-tags-updating-but-not-adding-history-after-switching-to-non-gvi-address-syntax/101591/7 "2025-01-30T00:56:44Z")

</div>

You're now receiving events from the device, instead of explicitly reading each point, and events typically have a timestamp included with them. The device has to be configured with the correct time.

---

<div class="post-metadata">

**Author:** ![tyler.bennett](https://avatars.discourse-cdn.com/v4/letter/t/f04885/32.png) [@tyler.bennett](https://forum.inductiveautomation.com/u/tyler.bennett)\
**Post date:** [January 30, 2025, 1:16am UTC](https://forum.inductiveautomation.com/t/dnp3-driver-tags-updating-but-not-adding-history-after-switching-to-non-gvi-address-syntax/101591/8 "2025-01-30T01:16:36Z")

</div>

> [@Kevin.Herron](#):
>
> The device has to be configured with the correct time.

Yes, I expect you are correct.  
I had foolishly thought that the Explicit Read operations previously used also had come with timestamps attached (perhaps not). I had also expected the device was previously being time synced, either through GPS IRIG or by syncing with the DNP master (Ignition).  
Its interesting that the device does show the correct "local" time on various status pages when using its configuration tool (SEL AcSELerator).  
I'm hunting for the correct status/settings, I'm not in these SEL devices that often.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [January 30, 2025, 1:18am UTC](https://forum.inductiveautomation.com/t/dnp3-driver-tags-updating-but-not-adding-history-after-switching-to-non-gvi-address-syntax/101591/9 "2025-01-30T01:18:37Z")

</div>

@msteele might have an idea where those settings are, I think he's got some experience with SEL stuff.

---

<div class="post-metadata">

**Author:** ![tyler.bennett](https://avatars.discourse-cdn.com/v4/letter/t/f04885/32.png) [@tyler.bennett](https://forum.inductiveautomation.com/u/tyler.bennett)\
**Post date:** [January 30, 2025, 11:48pm UTC](https://forum.inductiveautomation.com/t/dnp3-driver-tags-updating-but-not-adding-history-after-switching-to-non-gvi-address-syntax/101591/10 "2025-01-30T23:48:52Z")

</div>

> [@Kevin.Herron](#):
>
> The device has to be configured with the correct time.

The SEL-735 device is connected to a [SEL-2407 Satellite-Synchronized Clock  
 ](https://selinc.com/products/2407/) and every way that I have managed to query the SEL-735 device it appears to show correct time. More precisely is shows the local time (CST), without time zone indication.

My working theory is this...

**Observation:**

- When the current real-world time is `2025-01-30 17:07:22 CST` (UTC-6) SEL-735 Ignition shows the DNP events have timestamp `2025-01-30 11:07:22 CST` (UTC-12).

**Theory:**

- I suspect the SEL-735 device is timestamping the DNP events with local time (not UTC time), specifically Central time, CST, UTC-6 (six hours less than UTC).
- I suspect the Ignition DNP3 driver is expecting UTC timestamps and when the CST timestamp is received Ignition treats it as though it is a UTC timestamp, this makes the event timestamp, as recognized by Ignition six hours off.
- When ignition presents the event timestamp, which it thinks is a UTC timestamp it subtracts 6 hours to show the time as a CST timestamp. A UTC-12 timestamp being recognized/presented as a UTC-6 (CST) timestamp.

I did find a `UTC_OFF` setting in the SEL-735 which defines the offset between UTC and local time. Changing that had no effect on the DNP event timestamps recognized in Ignition.  
However I just found that the manual states this...  
_"The UTC\_OFF setting defines the offset between UTC and local time, **except when the time source is IRIG** and the IRIG type (setting TSTYPE) is set to IEEE. If TSTYPE = IEEE, the meter uses the UTC offset hours from the IRIG control bits. **In this case, the device requires IEEE C37.118 control bits to be included in the IRIG signal**."_

So now I suspect the [SEL-2407 Satellite-Synchronized Clock](https://selinc.com/products/2407/) is not sending the correct IEEE C37.118 control bits

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [January 31, 2025, 12:41am UTC](https://forum.inductiveautomation.com/t/dnp3-driver-tags-updating-but-not-adding-history-after-switching-to-non-gvi-address-syntax/101591/11 "2025-01-31T00:41:12Z")

</div>

The DNP3 spec uses UTC for the DNP3 time base. All timestamps are transmitted in UTC, and all receiving applications expect UTC.

There's no room for misinterpreting the timestamp received from a DNP3 outstation because it's transmitted and received in UTC, but it's certainly possible that it's simply wrong before it's transmitted.

---

<div class="post-metadata">

**Author:** ![tyler.bennett](https://avatars.discourse-cdn.com/v4/letter/t/f04885/32.png) [@tyler.bennett](https://forum.inductiveautomation.com/u/tyler.bennett)\
**Post date:** [January 31, 2025, 1:14am UTC](https://forum.inductiveautomation.com/t/dnp3-driver-tags-updating-but-not-adding-history-after-switching-to-non-gvi-address-syntax/101591/12 "2025-01-31T01:14:08Z")

</div>

> [@Kevin.Herron](#):
>
> it's certainly possible that it's simply wrong before it's transmitted.

Yes, its unclear to me how this happens but I'm just following the clues in an admittedly unfamiliar area. I'm feeling quite certain the issue is upstream of Ignition. Right now I'm looking into the possible impact of misconfigured dip switch settings on the SEL-2407 Satellite-Synchronized Clock as I suspect something odd is happening where the SEL-2407 is synching time to the SEL-735 and for some unknown reason the SEL-735 is interpreting local time (UTC-6) as being UTC time and timestamping DNP events with a UTC timestamp that is six hours off from what it should be.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/d/7d9353e14d81d3c046536d24a5e533ff481e9330.png)

- [SEL-2407 Satellite-Synchronized Clock Instruction Manual](https://selinc.com/api/download/3612/)
- [Description of IRIG Formats](https://www.meinbergglobal.com/english/info/irig.htm#formats)