# DNP3 Tags not backfilling data between class polls
**URL:** <https://forum.inductiveautomation.com/t/dnp3-tags-not-backfilling-data-between-class-polls/113858>\
**Created:** [February 9, 2026, 10:59pm UTC](https://forum.inductiveautomation.com/t/dnp3-tags-not-backfilling-data-between-class-polls/113858 "2026-02-09T22:59:57Z")\
**Showing post:** 33
**Post date:** [June 2, 2026, 6:21am UTC](https://forum.inductiveautomation.com/t/dnp3-tags-not-backfilling-data-between-class-polls/113858/33 "2026-06-02T06:21:49Z")
> [@Nol](#):
> ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/3/f/3f69a2340ed5f0097d4ca19116ad15846a3b9b80.png)
I recently tested DNP3 comms with a simulator ([GitHub - stepfunc/dnp3: Rust implementation of DNP3 (IEEE 1815) with idiomatic bindings for C, .NET, C++, and Java · GitHub](https://github.com/stepfunc/dnp3)) to see what's required for backfilling.
One thing that now jumps out at me from this screenshot is the wrong DNP3 data type: g32v5 = 32-bit (IEEE single-precision) floating-point numbers _ **without a time stamp** _.
For any DNP3 backfilling to work, I found the data types defined in the outstation must be set to vars that have timestamps.
E.g.
- AnalogueInput:
  - g32v3 (32bit int + timestamp) or
  - g32v5 (float + timestamp)
- BinaryInput:
  - g2v3 (value + timestamp)
- BinaryOutput:
  - g11v2 (value + timestamp)
- AnalogueOutput:
  - g42v3 (32bit int + timestamp)
  - g42v7 (float + timestamp)
Other than this, I got mine working by:
- Creating a Tag Group specifically for DNP3 tags with the settings ([from user manual](https://www.docs.inductiveautomation.com/docs/8.3/ignition-modules/opc-ua/opc-ua-drivers/dnp3/dnp3-driver#sequence-of-events))
  - OPC UA Queue Size: \> 1 (set to the max events to pull in)
  - OPC UA sampling interval: 0
- Tag History - Sample Mode: On Change
- Tags in Ignition must use the addresses exposed for the outstation via OPC UA (e.g. [outstation1]BinaryIn); you **cannot** use the direct "gvi" address (e.g. [outstation1]g32v5i3)
- DNP3 Device settings
  - Source Address: set to the Destination/Master address in the DNP3 Outstation - if this is not set, then unsolicited msgs won't be delivered here, and in some (all?) cases, requests for class data won't be responded to at all
  - Destination Address: set to the Outstation's DNP3 address
  - Class 1-3 polling: set these to the rates that you want to pull in events from these classes which will be stored in history.
  - Class 1-3 Unsolicited Event checkboxes: Check these to recieve class events as they happen. (This is not required to receive buffered events, it just hastens value updates)
- Set the event buffer size for each DNP3 data type in the outstation to appropriate values. These determine the max number of events to store in the outstation.
Note: you _do not_ need to check "Allow Back-fill Data" within the tag provider for backfilling to work.
_[View the full topic](https://forum.inductiveautomation.com/t/dnp3-tags-not-backfilling-data-between-class-polls/113858)._