I am using OPC-COM module as a data source, ignition as OPC UA gateway to tunnel data. this works great. and now I want to log those data, does historical tag feature take OPC-COM as a data source?

I have tried adding a Historical Tag Providers, by giving ignition OPC DA ProgId, and I doing it correctly?  
Is there a document that teach me how to set this up?

one more question, the tag providers status shows Demo Expired, do I need to acquire a license for this feature?

 ![](https://us1.discourse-cdn.com/inductiveautomation/original/2X/f/f0068716398255788becb77ff1fc5ff3eb2fd2bb.jpg)  
  
 ![](https://us1.discourse-cdn.com/inductiveautomation/original/2X/f/f9e63cbec726e72664dece7bd400072e6577b38d.jpg)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 10, 2015, 4:06pm UTC](https://forum.inductiveautomation.com/t/does-historical-tag-works-with-opc-com-module/9685/2 "2015-02-10T16:06:48Z")

</div>

In this set up you don’t want to use a historical tag provider, even though that sounds like a reasonable guess.

You would just make a UA connection to the gateway doing the tunneling, subscribe to tags like normal, and then enable history on them.

---

<div class="post-metadata">

**Author:** ![Colby.Clegg](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/colby.clegg/32/3282_2.png) [@Colby.Clegg](https://forum.inductiveautomation.com/u/Colby.Clegg)\
**Post date:** [February 10, 2015, 7:55pm UTC](https://forum.inductiveautomation.com/t/does-historical-tag-works-with-opc-com-module/9685/3 "2015-02-10T19:55:37Z")

</div>

To clarify a bit more, the tag history feature (which stores data to databases) requires the SQL Bridge module. That is why the demo is expiring.