# Driver Allen-Bradley

**URL:** <https://forum.inductiveautomation.com/t/driver-allen-bradley/74014>\
**Category:** Ignition\
**Tags:** ignition81\
**Created:** [May 22, 2023, 12:15pm UTC](https://forum.inductiveautomation.com/t/driver-allen-bradley/74014 "2023-05-22T12:15:30Z")\
**Posts on this page:** 10\
**Page:** 1

<div class="post-metadata">

**Author:** ![tecnoeletronic](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/tecnoeletronic/32/50975_2.png) [@tecnoeletronic](https://forum.inductiveautomation.com/u/tecnoeletronic)\
**Post date:** [May 22, 2023, 12:15pm UTC](https://forum.inductiveautomation.com/t/driver-allen-bradley/74014/1 "2023-05-22T12:15:30Z")

</div>

Hi,

i'm trying to read data from an AB PLC (see details on pictures) but without success.

 ![AB_CLX](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/5/f53ba3d7ffa7e48d00e16860799f1cd815281575.png)

Using the "Control Logix Legacy Driver" i cannot connect (Faulted Mode message)  
Using the "Allen-Bradley Logix Driver" the driver is connected but i cannot "browse" data (ok, it's an old firmware).

 ![AB_Diagnostics](https://us1.discourse-cdn.com/inductiveautomation/original/3X/b/b/bb65aea7f952157d87fa333e56ae29dad72e5b5a.png)

How i can define Tag's Paths manually? I can read data correctly using my custom driver (an old c# IEP driver implementation). I'm not an AB expert so i think that i'm missing somethings..

---

<div class="post-metadata">

**Author:** ![bschroeder](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/bschroeder/32/13260_2.png) [@bschroeder](https://forum.inductiveautomation.com/u/bschroeder)\
**Post date:** [May 22, 2023, 12:29pm UTC](https://forum.inductiveautomation.com/t/driver-allen-bradley/74014/2 "2023-05-22T12:29:42Z")

</div>

What are the firmware revisions of the PLCs you are trying to communicate with?

What is the physical comm path between the PLC and the Gateway?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [May 22, 2023, 12:36pm UTC](https://forum.inductiveautomation.com/t/driver-allen-bradley/74014/3 "2023-05-22T12:36:59Z")

</div>

Version 20.12 should work with the Legacy drivers, but that model needs the **CompactLogix** driver, not the **ControlLogix** driver.

---

<div class="post-metadata">

**Author:** ![tecnoeletronic](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/tecnoeletronic/32/50975_2.png) [@tecnoeletronic](https://forum.inductiveautomation.com/u/tecnoeletronic)\
**Post date:** [May 22, 2023, 12:39pm UTC](https://forum.inductiveautomation.com/t/driver-allen-bradley/74014/4 "2023-05-22T12:39:45Z")

</div>

Hi, thank for replies.

I added a CompactLogix Driver but the message is always the same.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/7/77f597ec6115949607c2101c6ac8ca80ff8bd3fe.png)

I would like to read some "GLOBAL" tags: 1 Integer and 3 strings.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [May 22, 2023, 12:44pm UTC](https://forum.inductiveautomation.com/t/driver-allen-bradley/74014/5 "2023-05-22T12:44:33Z")

</div>

Are there any errors in the wrapper logs?

Not sure what’s going on. Both drivers should work with this PLC and firmware version. Device must be in a weird state or not able to allocate more CIP connections or something.

You won’t be able to read tags unless the browse can be completed.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [May 22, 2023, 1:02pm UTC](https://forum.inductiveautomation.com/t/driver-allen-bradley/74014/6 "2023-05-22T13:02:14Z")

</div>

I'm now curious what [my alternate driver](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190) would get.

---

<div class="post-metadata">

**Author:** ![tecnoeletronic](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/tecnoeletronic/32/50975_2.png) [@tecnoeletronic](https://forum.inductiveautomation.com/u/tecnoeletronic)\
**Post date:** [May 22, 2023, 1:06pm UTC](https://forum.inductiveautomation.com/t/driver-allen-bradley/74014/7 "2023-05-22T13:06:47Z")

</div>

> LOGIXDriver \> Browse failed: status=0x05 [path destination unknown] , additional=[0x0000]

BACKPLANE = 0x01  
CPU SLOT = 0x00

But i think that it's a firewall problem.. i'm going to call the IT. I'll inform as soon as possible.

---

<div class="post-metadata">

**Author:** ![tecnoeletronic](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/tecnoeletronic/32/50975_2.png) [@tecnoeletronic](https://forum.inductiveautomation.com/u/tecnoeletronic)\
**Post date:** [May 23, 2023, 7:44am UTC](https://forum.inductiveautomation.com/t/driver-allen-bradley/74014/8 "2023-05-23T07:44:30Z")

</div>

Thi morning i'm going to try your alternate driver.. i will keep you informed.

---

<div class="post-metadata">

**Author:** ![tecnoeletronic](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/tecnoeletronic/32/50975_2.png) [@tecnoeletronic](https://forum.inductiveautomation.com/u/tecnoeletronic)\
**Post date:** [May 23, 2023, 7:52am UTC](https://forum.inductiveautomation.com/t/driver-allen-bradley/74014/9 "2023-05-23T07:52:50Z")

</div>

For your info: i asked to switch-on another similar machine and the Browe is working!  
I read that in some case it's necessary to re-download the SW on CPU to make it working..

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/b/0/b0520cb3e467f5ad451f431ab36d19a5dc396774.png)

---

<div class="post-metadata">

**Author:** ![Transistor](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/transistor/32/3380_2.png) [@Transistor](https://forum.inductiveautomation.com/u/Transistor)\
**Post date:** [May 2, 2025, 10:21am UTC](https://forum.inductiveautomation.com/t/driver-allen-bradley/74014/11 "2025-05-02T10:21:37Z")

</div>

sharan, please start a new thread. This thread is related to **connection to the PLC**. You seem to have already achieved this. You can delete your previous post and I'll delete this one.