# Easy Chart Tag Quality Going Bad Randomly

**URL:** <https://forum.inductiveautomation.com/t/easy-chart-tag-quality-going-bad-randomly/15908>\
**Category:** Ignition\
**Created:** [November 6, 2017, 11:27pm UTC](https://forum.inductiveautomation.com/t/easy-chart-tag-quality-going-bad-randomly/15908 "2017-11-06T23:27:27Z")\
**Posts on this page:** 10\
**Page:** 1

<div class="post-metadata">

**Author:** ![danewilbanks1](https://avatars.discourse-cdn.com/v4/letter/d/e274bd/32.png) [@danewilbanks1](https://forum.inductiveautomation.com/u/danewilbanks1)\
**Post date:** [November 6, 2017, 11:27pm UTC](https://forum.inductiveautomation.com/t/easy-chart-tag-quality-going-bad-randomly/15908/1 "2017-11-06T23:27:27Z")

</div>

I created an easy chart Friday with 5 tags coming in from PLC’s around the warehouse. I went through all of the settings recommended by Inductive, and different forum posts. I created the table seamlessly, with tag history enabled, and it ran for the remainder of the day. Coming in today, I see this error:  
Error running query:  
Tag Density Histogram Query  
Range: Mon Nov 06 15:00:00 MST 2017-\>Mon Nov 06 16:59:59 MST 2017  
Paths:  
tag  
tag  
tag  
tag  
tag  
@0ms  
On: Main Window.Root Container.Easy Chart

The chart is now red, and not reading any of the inputs. I have a SQL server running off of the data filtering through ignition using the transaction groups, and everything in regards to tag quality outside of this instance, seemingly points to no problem.  
I deleted the chart, and went through the steps/settings that I did last week, and it still comes up with this error.

On: Main Window.Root Container.Easy Chart  
caused by GatewayException: Error executing tag history query. Please verify that the connection is available, and that tag history is being stored to it.  
From details page of error:  
caused by Exception: Error executing tag history query. Please verify that the connection is available, and that tag history is being stored to it.

I’m on the trial version at the moment, but from my understanding that shouldn’t hinder me at all.  
Thanks so much in advance, I look forward to any input you guys have!

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [November 7, 2017, 2:23am UTC](https://forum.inductiveautomation.com/t/easy-chart-tag-quality-going-bad-randomly/15908/2 "2017-11-07T02:23:09Z")

</div>

> [@danewilbanks1](#):
>
> I'm on the trial version at the moment, but from my understanding that shouldn't hinder me at all.

Well, it'll hinder you every two hours when it stops recording....

---

<div class="post-metadata">

**Author:** ![danewilbanks1](https://avatars.discourse-cdn.com/v4/letter/d/e274bd/32.png) [@danewilbanks1](https://forum.inductiveautomation.com/u/danewilbanks1)\
**Post date:** [November 7, 2017, 11:15pm UTC](https://forum.inductiveautomation.com/t/easy-chart-tag-quality-going-bad-randomly/15908/3 "2017-11-07T23:15:11Z")

</div>

I’m aware of that. I was assuming that wasn’t the problem, given it’s worked through multiple refreshes of the trial period. My company hasn’t committed to a full purchase yet, so this is what I’m currently limited to.

---

<div class="post-metadata">

**Author:** ![paul-griffith](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul-griffith/32/37249_2.png) [@paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith)\
**Post date:** [November 7, 2017, 11:57pm UTC](https://forum.inductiveautomation.com/t/easy-chart-tag-quality-going-bad-randomly/15908/4 "2017-11-07T23:57:26Z")

</div>

Check the gateway’s logs (Status -\> Diagnostics -\> Logs) when you get this error on the client; there may be more information about why the query isn’t returning.

---

<div class="post-metadata">

**Author:** ![danewilbanks1](https://avatars.discourse-cdn.com/v4/letter/d/e274bd/32.png) [@danewilbanks1](https://forum.inductiveautomation.com/u/danewilbanks1)\
**Post date:** [November 8, 2017, 12:09am UTC](https://forum.inductiveautomation.com/t/easy-chart-tag-quality-going-bad-randomly/15908/5 "2017-11-08T00:09:32Z")

</div>

Where is the status selection that I’m looking for? Right clicking the graph and selecting “run diagnostics” returns this  
Checking Easy Chart…  
TagDensityQuery(tags=[[~]Totals/Cover Total, [~]Totals/Final Total, [~]Totals/Gear Total, [~]Totals/Stem Total, [~]Totals/Tripspring Total]): SQL Error  
TagHistoryQuery(tags=[prov:default:/tag:Totals/Cover Total, prov:default:/tag:Totals/Final Total, prov:default:/tag:Totals/Gear Total, prov:default:/tag:Totals/Stem Total, prov:default:/tag:Totals/Tripspring Total]): SQL Error

Saying that it’s a SQL error, however these tags are working flawlessly across both other parts of this project and the sql database. Any ideas?  
Thanks so much for the response!

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [November 8, 2017, 3:00am UTC](https://forum.inductiveautomation.com/t/easy-chart-tag-quality-going-bad-randomly/15908/6 "2017-11-08T03:00:22Z")

</div>

“Status =\> Diagnostics =\> Logs” is in the gateway web interface, not in the designer.

---

<div class="post-metadata">

**Author:** ![danewilbanks1](https://avatars.discourse-cdn.com/v4/letter/d/e274bd/32.png) [@danewilbanks1](https://forum.inductiveautomation.com/u/danewilbanks1)\
**Post date:** [November 8, 2017, 10:27pm UTC](https://forum.inductiveautomation.com/t/easy-chart-tag-quality-going-bad-randomly/15908/7 "2017-11-08T22:27:40Z")

</div>

DatasourceForwardTransaction 08Nov2017 15:26:58 Error forwarding data: Invalid object name ‘sqlth\_sce’.  
OpcUaConnection 08Nov2017 15:26:56 Keep Alive failureCount=83 exceeds failuresAllowed=1; disconnecting.  
OPC-UA Server.ReadService 08Nov2017 15:26:56 Returning ServiceFault for request: com.inductiveautomation.opcua.types.messages.ReadRequest@68640e58. StatusCode=StatusCode[Severity=Bad, Subcode=Bad\_SessionIdInvalid]  
MemoryForwardTransaction 08Nov2017 15:26:46 Error forwarding data: Invalid object name ‘sqlth\_sce’.  
OpcUaConnection 08Nov2017 15:26:46 Keep Alive failureCount=82 exceeds failuresAllowed=1; disconnecting.

I deleted some random tables that showed up in my SQL Database, and this was definitely the title to one of them. What does that entail?

---

<div class="post-metadata">

**Author:** ![paul-griffith](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul-griffith/32/37249_2.png) [@paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith)\
**Post date:** [November 8, 2017, 10:56pm UTC](https://forum.inductiveautomation.com/t/easy-chart-tag-quality-going-bad-randomly/15908/8 "2017-11-08T22:56:47Z")

</div>

Yes, the `sqlth_sce` (sql tag history \_ scan class executions) table is needed by default - particular for the ‘tag density query’ that the easy chart automatically runs (which fills in the date range slider).

If you don’t want Ignition’s historian to automatically flag ‘stale’ data (based on historical scan class execution rate) then you can go into the settings for the history provider (Configure → Tags → History) and at the bottom of the ‘advanced’ options uncheck the ‘Stale Data Detection’ flag:

 ![](https://us1.discourse-cdn.com/inductiveautomation/original/2X/9/99ea5e9b1c40345f647fd95f16e306ed30fd1bc9.png)

---

<div class="post-metadata">

**Author:** ![danewilbanks1](https://avatars.discourse-cdn.com/v4/letter/d/e274bd/32.png) [@danewilbanks1](https://forum.inductiveautomation.com/u/danewilbanks1)\
**Post date:** [November 8, 2017, 11:00pm UTC](https://forum.inductiveautomation.com/t/easy-chart-tag-quality-going-bad-randomly/15908/9 "2017-11-08T23:00:04Z")

</div>

I restarted the right module, to reinstate those tables that were deleted in my ignorance! Thank you so much. Everything’s up and groovy.

---

<div class="post-metadata">

**Author:** ![evan.tabor](https://avatars.discourse-cdn.com/v4/letter/e/94ad74/32.png) [@evan.tabor](https://forum.inductiveautomation.com/u/evan.tabor)\
**Post date:** [December 13, 2018, 5:56am UTC](https://forum.inductiveautomation.com/t/easy-chart-tag-quality-going-bad-randomly/15908/10 "2018-12-13T05:56:41Z")

</div>

> [@paul-griffith](#):
>
> torian to automatically flag 'stale' data (based on historical scan class execution rate) then you can go into the settings for the history provider

I have been fighting Deadlocks on sqlth\_sce for weeks, disabling this got everything moving again. Probably not the best long term solution, but I've got charts with data in them for tonight. I'm replying in case anyone comes across this same issue.