# Edge for stand alone HMI suggestions. Hardware&setup

**URL:** <https://forum.inductiveautomation.com/t/edge-for-stand-alone-hmi-suggestions-hardware-setup/58755>\
**Category:** Ignition\
**Tags:** vision, ignition81\
**Created:** [April 22, 2022, 4:04pm UTC](https://forum.inductiveautomation.com/t/edge-for-stand-alone-hmi-suggestions-hardware-setup/58755 "2022-04-22T16:04:16Z")\
**Posts on this page:** 7\
**Page:** 1

<div class="post-metadata">

**Author:** ![andrews](https://avatars.discourse-cdn.com/v4/letter/a/898d66/32.png) [@andrews](https://forum.inductiveautomation.com/u/andrews)\
**Post date:** [April 22, 2022, 4:04pm UTC](https://forum.inductiveautomation.com/t/edge-for-stand-alone-hmi-suggestions-hardware-setup/58755/1 "2022-04-22T16:04:16Z")

</div>

Hello,

I am retrofitting a panel. Basically need to add in my own screen and plc. Only thing is they need to be able to audit user actions:  
username,buttonClicked,timeStamp

And the regular run of the mill HMIs don’t really do that. So I was thinking to use Edge as a standalone.

What would be a easy ready to go edge screen I can pop into the panel?  
How would connecting to the plc go? Would I have to setup an isolated network in the panel? Ethernet or serial to the screen?

---

<div class="post-metadata">

**Author:** ![Arnaud\_Declerck](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/arnaud_declerck/32/44872_2.png) [@Arnaud\_Declerck](https://forum.inductiveautomation.com/u/Arnaud_Declerck)\
**Post date:** [April 22, 2022, 4:12pm UTC](https://forum.inductiveautomation.com/t/edge-for-stand-alone-hmi-suggestions-hardware-setup/58755/2 "2022-04-22T16:12:49Z")

</div>

Hi @andrews,

Did you check the ignition on board program.

> **[Ignition Onboard Solutions by Inductive Automation](https://www.inductiveautomation.com/onboard/)**
>
> Onboard devices come with Ignition or Ignition Edge by Inductive Automation installed & configured by approved manufacturers to jumpstart your digital projects.

There you can find panel pc with preloaded edge.

What the type of plc you need to connect to ?

Be aware that edge have only -+1week of logging available

Regards

---

<div class="post-metadata">

**Author:** ![andrews](https://avatars.discourse-cdn.com/v4/letter/a/898d66/32.png) [@andrews](https://forum.inductiveautomation.com/u/andrews)\
**Post date:** [April 22, 2022, 4:20pm UTC](https://forum.inductiveautomation.com/t/edge-for-stand-alone-hmi-suggestions-hardware-setup/58755/3 "2022-04-22T16:20:26Z")

</div>

I haven’t, but I am checking it out. And really whatever is easiest.

---

<div class="post-metadata">

**Author:** ![andrews](https://avatars.discourse-cdn.com/v4/letter/a/898d66/32.png) [@andrews](https://forum.inductiveautomation.com/u/andrews)\
**Post date:** [April 22, 2022, 4:33pm UTC](https://forum.inductiveautomation.com/t/edge-for-stand-alone-hmi-suggestions-hardware-setup/58755/4 "2022-04-22T16:33:27Z")

</div>

@Arnaud_Declerck , would I be able to save the audit log essentially to a database?

---

<div class="post-metadata">

**Author:** ![josborn](https://avatars.discourse-cdn.com/v4/letter/j/4bbf92/32.png) [@josborn](https://forum.inductiveautomation.com/u/josborn)\
**Post date:** [April 22, 2022, 5:25pm UTC](https://forum.inductiveautomation.com/t/edge-for-stand-alone-hmi-suggestions-hardware-setup/58755/5 "2022-04-22T17:25:23Z")

</div>

From the manual:

`Database access is disabled. This means that any database queries or bindings will not work, and the user sources that require a database connection will not be available. The Status and Configure pages of the Gateway Webpage have been updated to remove these features and reduce confusion. Despite this restriction, some "historical" storage can happen inside of Ignition.`

---

<div class="post-metadata">

**Author:** ![Arnaud\_Declerck](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/arnaud_declerck/32/44872_2.png) [@Arnaud\_Declerck](https://forum.inductiveautomation.com/u/Arnaud_Declerck)\
**Post date:** [April 22, 2022, 6:19pm UTC](https://forum.inductiveautomation.com/t/edge-for-stand-alone-hmi-suggestions-hardware-setup/58755/6 "2022-04-22T18:19:08Z")

</div>

@andrews the only way to save more than one week data is to synchronize edge with a full gateway.  
The only database available with edge is the internal one.

---

<div class="post-metadata">

**Author:** ![andrews](https://avatars.discourse-cdn.com/v4/letter/a/898d66/32.png) [@andrews](https://forum.inductiveautomation.com/u/andrews)\
**Post date:** [April 22, 2022, 6:53pm UTC](https://forum.inductiveautomation.com/t/edge-for-stand-alone-hmi-suggestions-hardware-setup/58755/7 "2022-04-22T18:53:37Z")

</div>

@Arnaud_Declerck thanks for the info.