# Edge Gateway fails to start

**URL:** <https://forum.inductiveautomation.com/t/edge-gateway-fails-to-start/68848>\
**Category:** Ignition\
**Tags:** vision\
**Created:** [January 20, 2023, 1:25pm UTC](https://forum.inductiveautomation.com/t/edge-gateway-fails-to-start/68848 "2023-01-20T13:25:04Z")\
**Posts on this page:** 1\
**Showing post:** 3

<div class="post-metadata">

**Author:** ![avaughn](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/avaughn/32/38972_2.png) [@avaughn](https://forum.inductiveautomation.com/u/avaughn)\
**Post date:** [January 20, 2023, 2:14pm UTC](https://forum.inductiveautomation.com/t/edge-gateway-fails-to-start/68848/3 "2023-01-20T14:14:57Z")

</div>

This looks familiar. I believe the trust store was corrupted. You should be able to follow the steps below to get back into a working state.

1. Navigate to the `C:\Program Files\Inductive Automation\Ignition\lib\runtime\jre-win\lib\security` directory.
2. Make a copy of the cacerts and cacerts.bak files and place in another directory. (They shouldn't be needed but I like to make copies before deleting files)
3. Delete the cacerts file from its original directory.
4. Re-name the cacerts.bak file to cacerts.
5. Use the stop-ignition.bat file to stop the Ignition service.
6. Use the start-ignition.bat file to start the Ignition service again.

For steps 5 and 6, you can also stop/start the service from Windows Services.

---