Yes, unfortunately this is due to a bug in FreeOpcUa that has not been fixed yet.

When we browse to discover the TypeDefinition of a Node FreeOpcUa returns no references, and this ends up forcing us to treat the Node as a base VariableNode, but in your case this is being called from some higher level code that expects correct modelling constraints.

It also manifests in simpler scenarios: [[milo-dev] server status node has wrong type](https://www.eclipse.org/lists/milo-dev/msg01041.html)

The code in this gist reproduces the issue: [Scratch.java · GitHub](https://gist.github.com/kevinherron/75ebdca52bbaf4fc433c0886c00208bc)

---