When I start a group I get this error message about 20 times, then after that it works without any problems.

Group Execution Error  
Error executing item NextTestOutNumber: Object reference not set to an instance of an object.

This group looks at a table on the SQL server and looks at the last “test out” number recorded. When a machine is started for non-processes mode, basically to test it, I automatically assign a test out number. FSQL looks at the last number, adds 1 to it, and then sends the resulting number to the PLC. It functions perfectly during normal operation. It’s just when I start the group that I get error messages, and they just stop coming after a few seconds.

I can give more detail of how the group functions if you need.

---

<div class="post-metadata">

**Author:** ![SonicClang](https://avatars.discourse-cdn.com/v4/letter/s/eada6e/32.png) [@SonicClang](https://forum.inductiveautomation.com/u/SonicClang)\
**Post date:** [May 6, 2009, 7:25pm UTC](https://forum.inductiveautomation.com/t/error-message-when-group-starts/1138/2 "2009-05-06T19:25:31Z")

</div>

Ah! Never mind, I had an action item set to ignore the group trigger. I disabled that and it’s fine now.