# Error read/write Siemens Tag

**URL:** <https://forum.inductiveautomation.com/t/error-read-write-siemens-tag/69769>\
**Category:** Ignition\
**Tags:** ignition81\
**Created:** [February 13, 2023, 11:11am UTC](https://forum.inductiveautomation.com/t/error-read-write-siemens-tag/69769 "2023-02-13T11:11:22Z")\
**Posts on this page:** 3\
**Page:** 2

<div class="post-metadata">

**Author:** ![indenkleefj](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/indenkleefj/32/10961_2.png) [@indenkleefj](https://forum.inductiveautomation.com/u/indenkleefj)\
**Post date:** [September 14, 2023, 2:39pm UTC](https://forum.inductiveautomation.com/t/error-read-write-siemens-tag/69769/21 "2023-09-14T14:39:46Z")

</div>

Thank you for the help.  
If Ignition will be the only application writing the values (in the future).  
Is there a way to correct the values in the PLC without opening the actual PLC program?  
For example, if we first empty the string and then start writing them with Ignition.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [September 14, 2023, 2:50pm UTC](https://forum.inductiveautomation.com/t/error-read-write-siemens-tag/69769/22 "2023-09-14T14:50:09Z")

</div>

I’d expect writing new string values from Ignition to correct the issue as long as whatever other process that wrote incorrect values doesn’t do it again.

---

<div class="post-metadata">

**Author:** ![indenkleefj](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/indenkleefj/32/10961_2.png) [@indenkleefj](https://forum.inductiveautomation.com/u/indenkleefj)\
**Post date:** [September 15, 2023, 2:33pm UTC](https://forum.inductiveautomation.com/t/error-read-write-siemens-tag/69769/23 "2023-09-15T14:33:48Z")

</div>

I can confirm that writing an empty string will resolve the problem.

[Previous page](https://forum.inductiveautomation.com/t/error-read-write-siemens-tag/69769.md?page=1)