Hello,

I’m accessing Input tags of MicroLogix 1100 and found that i can not write to Input Tags (I:0/0 etc)  
However, i can write to memory tag like N7 or B3.

I’ve checked all the necessary setting and it all set in Read/Write Mode

Could you please tell me what am i missing? Or is it because the tags are physical tags hence you could not “write” to it.

thx

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [September 21, 2019, 3:01am UTC](https://forum.inductiveautomation.com/t/error-writing-bad-unsupported-micrologix-1100/28421/2 "2019-09-21T03:01:41Z")

</div>

Inputs are typically read-only. Apparently this applies to your Micro1100. Even if it let you write to it, the value would be immediately replaced by the actual physical input…