# Extra OPC Folder

**URL:** <https://forum.inductiveautomation.com/t/extra-opc-folder/35094>\
**Category:** Ignition\
**Tags:** ignition79\
**Created:** [May 27, 2020, 5:59pm UTC](https://forum.inductiveautomation.com/t/extra-opc-folder/35094 "2020-05-27T17:59:08Z")\
**Posts on this page:** 4\
**Page:** 1

<div class="post-metadata">

**Author:** ![blueweb00](https://avatars.discourse-cdn.com/v4/letter/b/d07c76/32.png) [@blueweb00](https://forum.inductiveautomation.com/u/blueweb00)\
**Post date:** [May 27, 2020, 5:59pm UTC](https://forum.inductiveautomation.com/t/extra-opc-folder/35094/1 "2020-05-27T17:59:08Z")

</div>

In the picture, for REAL[3].R9, there is an extra folder to assign it to an Ignition tag. But for REAL[4].R9, there is not an extra folder. Is this problem occurring because of Ignition, or due to RSLogix?

This problem occurs when I edit a controller tag through RSLogix 5000. I started out with 1-10, and needed to change it to 0-9. The REAL that is not currently being used does not have this problem, but the tags I am currently using, I have to search into another folder. REAL[3].R9.R9.

7.9.12

![OPC Folder](https://us1.discourse-cdn.com/inductiveautomation/original/2X/5/5fef97bae726f39f7dd07e862c9cbed6b87433b9.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [May 27, 2020, 6:03pm UTC](https://forum.inductiveautomation.com/t/extra-opc-folder/35094/2 "2020-05-27T18:03:21Z")

</div>

Is this a screenshot of the OPC browser?

If this is the legacy driver you may just need to restart the OPC UA module.

---

<div class="post-metadata">

**Author:** ![blueweb00](https://avatars.discourse-cdn.com/v4/letter/b/d07c76/32.png) [@blueweb00](https://forum.inductiveautomation.com/u/blueweb00)\
**Post date:** [May 27, 2020, 6:19pm UTC](https://forum.inductiveautomation.com/t/extra-opc-folder/35094/3 "2020-05-27T18:19:50Z")

</div>

Yes, that is OPC browser.

I will try that. Will restarting the module disable all tags from operating?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [May 27, 2020, 6:30pm UTC](https://forum.inductiveautomation.com/t/extra-opc-folder/35094/4 "2020-05-27T18:30:34Z")

</div>

You’ll lose connection to your PLCs and values while it restarts. You might need to wait if that’s not okay.