We have had some components with known memory leaks in the past, although the bulk of those were fixed in the last release. Can you tell us more about your setup so we can help? Thanks.

---

<div class="post-metadata">

**Author:** ![ynejati](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ynejati/32/6093_2.png) [@ynejati](https://forum.inductiveautomation.com/u/ynejati)\
**Post date:** [August 17, 2019, 5:12am UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/43 "2019-08-17T05:12:01Z")

</div>

The Alarm Status Table pulls alarm data from the Gateway. It can not be set up to connect to a database. Would the standard Table component be a better fit for you? With some configuration, you can set it up to behave similarly to the Alarm Status Table since they are both built on the same foundation. Feel free to check out this [thread](http://forum.inductiveautomation.com/t/feedback-new-perspective-table) and let us know if you have any questions.

---

<div class="post-metadata">

**Author:** ![miltonrodas360](https://avatars.discourse-cdn.com/v4/letter/m/4491bb/32.png) [@miltonrodas360](https://forum.inductiveautomation.com/u/miltonrodas360)\
**Post date:** [August 20, 2019, 1:03pm UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/44 "2019-08-20T13:03:52Z")

</div>

I sent in the wrapper logs in with a support ticket as well. It seems that there perspective tries to load fire an event model that does not exist. In the meantime we have resorted to designing a table component. As long as I am able to show my client that they can view their system on web browser on the fly is vital . Thank you!

---

<div class="post-metadata">

**Author:** ![vcgasman](https://avatars.discourse-cdn.com/v4/letter/v/ecc23a/32.png) [@vcgasman](https://forum.inductiveautomation.com/u/vcgasman)\
**Post date:** [August 20, 2019, 1:14pm UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/45 "2019-08-20T13:14:03Z")

</div>

Any update on this please? (Marquee Mode)

---

<div class="post-metadata">

**Author:** ![lasse](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/lasse/32/11108_2.png) [@lasse](https://forum.inductiveautomation.com/u/lasse)\
**Post date:** [August 20, 2019, 2:21pm UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/46 "2019-08-20T14:21:45Z")

</div>

Is there a way to make filtered “Shelved” alarms? I currently have 2 projects, where they can’t see each other alarms.

It works fine for the active alarms, but the shelved ones (the counter) appear on both.

Is there a workaround for this?

---

<div class="post-metadata">

**Author:** ![miltonrodas360](https://avatars.discourse-cdn.com/v4/letter/m/4491bb/32.png) [@miltonrodas360](https://forum.inductiveautomation.com/u/miltonrodas360)\
**Post date:** [August 23, 2019, 2:30pm UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/47 "2019-08-23T14:30:54Z")

</div>

The best solution we found was to create our own table and setup our own filters and headers. The current alarm status table creates too many bugs. Our memory and cpu load went from 99% to around an average of 5% by creating our own alarm status table.

---

<div class="post-metadata">

**Author:** ![ynejati](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ynejati/32/6093_2.png) [@ynejati](https://forum.inductiveautomation.com/u/ynejati)\
**Post date:** [August 23, 2019, 2:42pm UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/48 "2019-08-23T14:42:32Z")

</div>

Hi,

Sorry for the delay. Yes, we will include something like this for phase 2 of the Alarm Status Table. It was planned to add the pager to the AST, the same one that the Table component uses, but I think adding a built in marquee mode is a good idea.

-Y

---

<div class="post-metadata">

**Author:** ![ynejati](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ynejati/32/6093_2.png) [@ynejati](https://forum.inductiveautomation.com/u/ynejati)\
**Post date:** [August 23, 2019, 2:47pm UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/49 "2019-08-23T14:47:03Z")

</div>

Hi,

Sorry to hear about this. Support has certainly made us aware of the memory and cpu issue you reported. What other bugs or issues have you encountered?

-Y

---

<div class="post-metadata">

**Author:** ![miltonrodas360](https://avatars.discourse-cdn.com/v4/letter/m/4491bb/32.png) [@miltonrodas360](https://forum.inductiveautomation.com/u/miltonrodas360)\
**Post date:** [August 23, 2019, 2:54pm UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/50 "2019-08-23T14:54:26Z")

</div>

Here is another issue we are having: some tags show up as “bad\_failure” even though we have double and triple checked the opc and tag config. Not sure what is causing this:

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/2/2ac643036faf7ba6790be050682d448a4c6046d2.png) . Any clue what could be causing this?

---

<div class="post-metadata">

**Author:** ![vcgasman](https://avatars.discourse-cdn.com/v4/letter/v/ecc23a/32.png) [@vcgasman](https://forum.inductiveautomation.com/u/vcgasman)\
**Post date:** [August 30, 2019, 5:21pm UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/51 "2019-08-30T17:21:29Z")

</div>

Hi-  
Is there any way to access additional columns for the Shelved tab? I realize you are providing the same 3 that exist in Vision but it would be a nice feature to be able to display at least the Display Path in the shelved table. I tried adding the same named arrays as in the active array but nothing gets filled in when viewing the table, only the column header names. My customer just asked me to remove the sourcePath from the active alarm table because it doesn’t mean much to them. In the shelved table, this is the only identifier of what alarm was shelved.  
Thanks-

 ![shelvedalms](https://us1.discourse-cdn.com/inductiveautomation/original/2X/a/a1a5a07c5d8fb7d72371b51b6e123e1354e93f5a.jpeg)

---

<div class="post-metadata">

**Author:** ![ynejati](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ynejati/32/6093_2.png) [@ynejati](https://forum.inductiveautomation.com/u/ynejati)\
**Post date:** [September 6, 2019, 3:13pm UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/52 "2019-09-06T15:13:36Z")

</div>

Hi,

I am not sure. But others might be able to help. If you don’t mind making a separate post in the forum regarding this issue that would be great. Thanks!

-Y

---

<div class="post-metadata">

**Author:** ![ynejati](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ynejati/32/6093_2.png) [@ynejati](https://forum.inductiveautomation.com/u/ynejati)\
**Post date:** [September 6, 2019, 3:15pm UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/53 "2019-09-06T15:15:25Z")

</div>

Hi,

No, not currently. But we can consider this in phase 2 which should be happening soon. I will add this to the list. Thanks for letting us know.

-Y

---

<div class="post-metadata">

**Author:** ![ynejati](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ynejati/32/6093_2.png) [@ynejati](https://forum.inductiveautomation.com/u/ynejati)\
**Post date:** [September 16, 2019, 9:13pm UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/54 "2019-09-16T21:13:05Z")

</div>

Unpinned on September 16, 2019, 9:13pm UTC



---

<div class="post-metadata">

**Author:** ![alo.go](https://avatars.discourse-cdn.com/v4/letter/a/bb73d2/32.png) [@alo.go](https://forum.inductiveautomation.com/u/alo.go)\
**Post date:** [October 31, 2019, 3:35pm UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/55 "2019-10-31T15:35:06Z")

</div>

It is possible to translate the name of the alarm?  
it is possible to remove the “details” button?  
it is possible to remove the “settings” button??  
It is possible to remove the “SHELVED” tab??

---

<div class="post-metadata">

**Author:** ![ynejati](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ynejati/32/6093_2.png) [@ynejati](https://forum.inductiveautomation.com/u/ynejati)\
**Post date:** [November 11, 2019, 3:30pm UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/56 "2019-11-11T15:30:59Z")

</div>

The answer to all of your questions, is no, not yet. We do plan to apply translations to the table components sometime soon. Regarding your requests to remove specific items, I will add these to the list, and do my best to include them in the current work on the alarm status table and implementation of the alarm journal table. Currently this work has been placed on pause, as we work on more pressings items, but should resume this week.

---

<div class="post-metadata">

**Author:** ![denis.palomanes](https://avatars.discourse-cdn.com/v4/letter/d/779978/32.png) [@denis.palomanes](https://forum.inductiveautomation.com/u/denis.palomanes)\
**Post date:** [November 12, 2019, 4:51pm UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/57 "2019-11-12T16:51:30Z")

</div>

Hello,

We have a customer that wants the perspective module, but in this project we have the alarm status table and we can not translate it, so when you say “soon” for when can we estimate the date? end of the year? begining of next year? 2021…? can you give us a more specific answer?

Thank you,

---

<div class="post-metadata">

**Author:** ![fisayoa](https://avatars.discourse-cdn.com/v4/letter/f/5f9b8f/32.png) [@fisayoa](https://forum.inductiveautomation.com/u/fisayoa)\
**Post date:** [November 18, 2019, 10:10am UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/58 "2019-11-18T10:10:07Z")

</div>

Hi,  
Please, any idea where I can configure the Alarm details? … It pops up empty.  
I have ignition 8.0.4 installed.  
Tags are located on 7.9.12 Gateway  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/3/3e6404922a7d983c64aaa445ed686cd480c8462b.png)

---

<div class="post-metadata">

**Author:** ![NorthPoint](https://avatars.discourse-cdn.com/v4/letter/n/a88e4f/32.png) [@NorthPoint](https://forum.inductiveautomation.com/u/NorthPoint)\
**Post date:** [December 5, 2019, 10:26pm UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/59 "2019-12-05T22:26:38Z")

</div>

Good afternoon. I am working on the same project that vcgasman asked this question about back in August. We still need to be able to sort by default by active time first…is that possible yet? Any ETA on it, if not?

Thanks…

---

<div class="post-metadata">

**Author:** ![amirsalar.arya.kia](https://avatars.discourse-cdn.com/v4/letter/a/d26b3c/32.png) [@amirsalar.arya.kia](https://forum.inductiveautomation.com/u/amirsalar.arya.kia)\
**Post date:** [December 19, 2019, 9:39pm UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/60 "2019-12-19T21:39:54Z")

</div>

Hi,  
I made a separate post but thought I take my chances here as well! The Alarm Status Table in perspective doesn’t poll my alarms while the same component in vision does. Any ideas?  
Cheers,

---

<div class="post-metadata">

**Author:** ![paul-griffith](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul-griffith/32/37249_2.png) [@paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith)\
**Post date:** [December 19, 2019, 9:48pm UTC](https://forum.inductiveautomation.com/t/feedback-new-perspective-alarm-status-table/25273/61 "2019-12-19T21:48:10Z")

</div>

It’s a known issue, should be fixed pretty soon.