I'm using Omron FIN/TCP to read DM area which data type is a float, it returns a wrong value (negative number) but the same DM returns a good float value when using Kepware.

Does IA Omron driver support float? or am I missing something?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 23, 2023, 2:19pm UTC](https://forum.inductiveautomation.com/t/float-data-type-in-omron-driver/70201/2 "2023-02-23T14:19:15Z")

</div>

This area is 16-bit. You would need to use the Float DataType designator in your address.

`D<Float>0` or something like that. See [Omron FINS Driver - Ignition User Manual 8.1 - Ignition Documentation](https://docs.inductiveautomation.com/display/DOC81/Omron+FINS+Driver#OmronFINSDriver-Addressing)