> [@Stef\_Velers](#):
>
> so instead of reading the tag 20 times

Yes, we covered that [yesterday](https://forum.inductiveautomation.com/t/gateway-scripts-or-expression/83077/18) where you were running 48 × `readBlocking` which will run one after another with each waiting until it is finished before going on to the next one. Read them all at once if at all possible. (There will be a maximum limit - but it will be large.)

---