# GAN connections status with redundant gateway?

**URL:** <https://forum.inductiveautomation.com/t/gan-connections-status-with-redundant-gateway/65709>\
**Category:** Ignition\
**Tags:** ignition81\
**Created:** [October 26, 2022, 3:56pm UTC](https://forum.inductiveautomation.com/t/gan-connections-status-with-redundant-gateway/65709 "2022-10-26T15:56:44Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![mazeyrat](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/mazeyrat/32/10955_2.png) [@mazeyrat](https://forum.inductiveautomation.com/u/mazeyrat)\
**Post date:** [October 26, 2022, 3:56pm UTC](https://forum.inductiveautomation.com/t/gan-connections-status-with-redundant-gateway/65709/1 "2022-10-26T15:56:45Z")

</div>

**Ignition 8.1.21**

is there any System tags for the gateway (outgoing) connections Status.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/a/f/af8ae447a872b0d30edb336f6b94e63aa4365540.png)

10.100.3.143 is a redundant gateway.  
My backup server is not started.

what does means:  
**\_0:0 and \_1:0**

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/4/5/45f34441445af106262407129c77c3fed5adf8a3.png)

---

<div class="post-metadata">

**Author:** ![Muhammad\_Musarrat](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/muhammad_musarrat/32/40074_2.png) [@Muhammad\_Musarrat](https://forum.inductiveautomation.com/u/Muhammad_Musarrat)\
**Post date:** [October 26, 2022, 10:26pm UTC](https://forum.inductiveautomation.com/t/gan-connections-status-with-redundant-gateway/65709/2 "2022-10-26T22:26:51Z")

</div>

Have you tried looking at the tag [System]Gateway/Redundancy/Connection/IsConnected?

---

<div class="post-metadata">

**Author:** ![mazeyrat](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/mazeyrat/32/10955_2.png) [@mazeyrat](https://forum.inductiveautomation.com/u/mazeyrat)\
**Post date:** [October 27, 2022, 2:48pm UTC](https://forum.inductiveautomation.com/t/gan-connections-status-with-redundant-gateway/65709/3 "2022-10-27T14:48:54Z")

</div>

Yes, the tag you mention is ok for the Connection status beetween of the 2 nodes of a redundant gateway.

In my use case, I have a **"scaleout"** architecture whith a front end server a some redundant tag and IO servers.

I would like to monitor the GAN connection between the front end gateway and others gateway

**Gateway/Gateway Network/..** system tags from the front end server are not very explicit...