# Gateway JVM terminated when IEC 61850 device was power-cycled (8.1.49, Linux)

**URL:** <https://forum.inductiveautomation.com/t/gateway-jvm-terminated-when-iec-61850-device-was-power-cycled-8-1-49-linux/117554>\
**Category:** Ignition\
**Tags:** perspective\
**Created:** [October 21, 2026, 4:17am UTC](https://forum.inductiveautomation.com/t/gateway-jvm-terminated-when-iec-61850-device-was-power-cycled-8-1-49-linux/117554 "2026-10-21T04:17:15Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![jhs](https://avatars.discourse-cdn.com/v4/letter/j/c67d28/32.png) [@jhs](https://forum.inductiveautomation.com/u/jhs)\
**Post date:** [October 21, 2026, 4:17am UTC](https://forum.inductiveautomation.com/t/gateway-jvm-terminated-when-iec-61850-device-was-power-cycled-8-1-49-linux/117554/1 "2026-10-21T04:17:15Z")

</div>

Hi all,

Sharing an issue we hit on a data center EPMS project, in case it helps  
others using the IEC 61850 driver on Linux.

**Environment**

- Ignition 8.1.49 on Linux [distro/version]
- EPMS gateway connected to [N] IEDs via the IEC 61850 driver
- DCIM and BMS gateways connect to the EPMS gateway over OPC UA

**What happened**  
During electrical safety testing, the IEC 61850 communication equipment  
was switched OFF and back ON. At that moment the EPMS gateway JVM  
terminated, and the service wrapper relaunched it about 6 seconds later.  
While it was down, the OPC UA connections from the DCIM and BMS gateways  
went into error. This happened on two consecutive test days.

**wrapper.log excerpt**  
[paste log here]

**What we found so far**  
Our analysis points to file descriptor (FD) range handling in the native  
(TMW) communication code the IEC 61850 driver uses on Linux.

**Workaround under evaluation**  
Replacing IEC 61850 with Modbus TCP for these devices. In our setup,  
millisecond timestamps are not coming through from the devices anyway.

**Questions**

1. Has anyone else seen the gateway go down on IEC 61850 device reconnects on Linux?
2. Is this addressed in a later 8.1.x or 8.3 release?
3. Any recommended mitigation (e.g., open-files ulimit) until a fix is available?