# Gateway Redundancy Server Location

**URL:** <https://forum.inductiveautomation.com/t/gateway-redundancy-server-location/70476>\
**Category:** Ignition\
**Tags:** ignition81\
**Created:** [March 1, 2023, 2:52pm UTC](https://forum.inductiveautomation.com/t/gateway-redundancy-server-location/70476 "2023-03-01T14:52:00Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![j.israelsen](https://avatars.discourse-cdn.com/v4/letter/j/ad7895/32.png) [@j.israelsen](https://forum.inductiveautomation.com/u/j.israelsen)\
**Post date:** [March 1, 2023, 2:52pm UTC](https://forum.inductiveautomation.com/t/gateway-redundancy-server-location/70476/1 "2023-03-01T14:52:00Z")

</div>

Generally we have setup our gateway redundancy to be at the same location. However, can redundancy be setup for gateways at two separate locations? If so, what sort of concerns are there? Is it even a supported type of configuration?

---

<div class="post-metadata">

**Author:** ![andrews](https://avatars.discourse-cdn.com/v4/letter/a/898d66/32.png) [@andrews](https://forum.inductiveautomation.com/u/andrews)\
**Post date:** [March 1, 2023, 2:58pm UTC](https://forum.inductiveautomation.com/t/gateway-redundancy-server-location/70476/2 "2023-03-01T14:58:45Z")

</div>

Yes it can.

See [System Architectures - Ignition User Manual 8.1 - Ignition Documentation (inductiveautomation.com)](https://docs.inductiveautomation.com/display/DOC81/System+Architectures)

Obviously, the biggest concern is maintaining comms to remote redundant gateway.

---

<div class="post-metadata">

**Author:** ![bschroeder](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/bschroeder/32/13260_2.png) [@bschroeder](https://forum.inductiveautomation.com/u/bschroeder)\
**Post date:** [March 1, 2023, 2:59pm UTC](https://forum.inductiveautomation.com/t/gateway-redundancy-server-location/70476/3 "2023-03-01T14:59:24Z")

</div>

Biggest thing would be comms from the secondary site to the PLCs. If the secondary becomes active, and the latency from the secondary gateway to the PLCs is high, then communications will suffer.