# Gateway service error 1067

**URL:** <https://forum.inductiveautomation.com/t/gateway-service-error-1067/6792>\
**Category:** Ignition\
**Created:** [June 28, 2013, 2:27pm UTC](https://forum.inductiveautomation.com/t/gateway-service-error-1067/6792 "2013-06-28T14:27:20Z")\
**Posts on this page:** 6\
**Page:** 1

<div class="post-metadata">

**Author:** ![rcorkern](https://avatars.discourse-cdn.com/v4/letter/r/90db22/32.png) [@rcorkern](https://forum.inductiveautomation.com/u/rcorkern)\
**Post date:** [June 28, 2013, 2:27pm UTC](https://forum.inductiveautomation.com/t/gateway-service-error-1067/6792/1 "2013-06-28T14:27:20Z")

</div>

Prompted to update Java 7 to update 25 so I did. Upon reboot when launching the project I’m still prompted everytime to update Java even though I have updated and even completely removed and re-installed.  
After a few tries of getting Java to work I then noticed that the Gateway service no longer starts.  
Here’s the the wrapper log.  
Thanks in advance!  
[wrapper.log](https://us1.discourse-cdn.com/inductiveautomation/original/2X/d/d72349e9434c56515af8716faea766e12da76701.log) (4.78 MB)

---

<div class="post-metadata">

**Author:** ![rcorkern](https://avatars.discourse-cdn.com/v4/letter/r/90db22/32.png) [@rcorkern](https://forum.inductiveautomation.com/u/rcorkern)\
**Post date:** [June 28, 2013, 2:37pm UTC](https://forum.inductiveautomation.com/t/gateway-service-error-1067/6792/2 "2013-06-28T14:37:11Z")

</div>

I see where the path to Java is incorrect but how can I change it?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [June 28, 2013, 3:14pm UTC](https://forum.inductiveautomation.com/t/gateway-service-error-1067/6792/3 "2013-06-28T15:14:42Z")

</div>

In the ‘data’ directory there’s a file called ignition.conf that has the ‘wrapper.java.command’ variable.

---

<div class="post-metadata">

**Author:** ![rcorkern](https://avatars.discourse-cdn.com/v4/letter/r/90db22/32.png) [@rcorkern](https://forum.inductiveautomation.com/u/rcorkern)\
**Post date:** [June 28, 2013, 4:03pm UTC](https://forum.inductiveautomation.com/t/gateway-service-error-1067/6792/4 "2013-06-28T16:03:35Z")

</div>

ok, I was able to correct the path but the gateway service still cannot be started

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [June 28, 2013, 4:10pm UTC](https://forum.inductiveautomation.com/t/gateway-service-error-1067/6792/5 "2013-06-28T16:10:20Z")

</div>

Can you post the logs again?

---

<div class="post-metadata">

**Author:** ![rcorkern](https://avatars.discourse-cdn.com/v4/letter/r/90db22/32.png) [@rcorkern](https://forum.inductiveautomation.com/u/rcorkern)\
**Post date:** [June 28, 2013, 4:23pm UTC](https://forum.inductiveautomation.com/t/gateway-service-error-1067/6792/6 "2013-06-28T16:23:28Z")

</div>

Ah nice catch. I guess I didnt save the updated path. I saved it and rebooted and the service started up fine! Thank you!