A customer has a bunch of new GE PLCs and a new iFix SCADA system, but is very interested in Ignition:

- Can you provide some suggestions for a drive to connect the PLCs to Ignition?
- Is iFix an OPC server to which Ignition can connect?

Any suggestions are greatly appreciated. I apologize for the lack of details.

---

<div class="post-metadata">

**Author:** ![Dravik](https://avatars.discourse-cdn.com/v4/letter/d/e274bd/32.png) [@Dravik](https://forum.inductiveautomation.com/u/Dravik)\
**Post date:** [October 26, 2012, 3:32pm UTC](https://forum.inductiveautomation.com/t/ge-plc-ifix-questions/5336/2 "2012-10-26T15:32:16Z")

</div>

We use Kepware to connect our 9070 and 9030’s to Ignition.

iFix 4.0 and up all can be connected to via OPC. I do it here quite a bit. You can see both the local database and any network connected databases through the OPC interface.

- Dravik

---

<div class="post-metadata">

**Author:** ![Michael.Stofan](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.stofan/32/3342_2.png) [@Michael.Stofan](https://forum.inductiveautomation.com/u/Michael.Stofan)\
**Post date:** [October 26, 2012, 11:51pm UTC](https://forum.inductiveautomation.com/t/ge-plc-ifix-questions/5336/3 "2012-10-26T23:51:22Z")

</div>

Dravik’s got it. We see Kepware used quite a bit when we have a PLC Ignition doesn’t have a native driver for.

As for connecting to iFix, you may need the OPC-COM module if it’s a OPC-DCOM server. Other than that, you should be fine!

---

<div class="post-metadata">

**Author:** ![Dravik](https://avatars.discourse-cdn.com/v4/letter/d/e274bd/32.png) [@Dravik](https://forum.inductiveautomation.com/u/Dravik)\
**Post date:** [October 29, 2012, 1:23am UTC](https://forum.inductiveautomation.com/t/ge-plc-ifix-questions/5336/4 "2012-10-29T01:23:07Z")

</div>

[quote=“michael.stofan”]Dravik’s got it. We see Kepware used quite a bit when we have a PLC Ignition doesn’t have a native driver for.

As for connecting to iFix, you may need the OPC-COM module if it’s a OPC-DCOM server. Other than that, you should be fine![/quote]

Michael -

It is indeed a DCOM server.

---

<div class="post-metadata">

**Author:** ![Michael.Stofan](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.stofan/32/3342_2.png) [@Michael.Stofan](https://forum.inductiveautomation.com/u/Michael.Stofan)\
**Post date:** [October 30, 2012, 9:41pm UTC](https://forum.inductiveautomation.com/t/ge-plc-ifix-questions/5336/5 "2012-10-30T21:41:38Z")

</div>

Good to know, thanks!