# How do I connect Endress+Hauser Liquiline CM-448 controllers with Profinet output to Ignition?

**URL:** <https://forum.inductiveautomation.com/t/how-do-i-connect-endress-hauser-liquiline-cm-448-controllers-with-profinet-output-to-ignition/71376>\
**Category:** Ignition\
**Created:** [March 21, 2023, 1:55pm UTC](https://forum.inductiveautomation.com/t/how-do-i-connect-endress-hauser-liquiline-cm-448-controllers-with-profinet-output-to-ignition/71376 "2023-03-21T13:55:41Z")\
**Posts on this page:** 6\
**Page:** 1

<div class="post-metadata">

**Author:** ![Matthew\_McBride](https://avatars.discourse-cdn.com/v4/letter/m/a698b9/32.png) [@Matthew\_McBride](https://forum.inductiveautomation.com/u/Matthew_McBride)\
**Post date:** [March 21, 2023, 1:55pm UTC](https://forum.inductiveautomation.com/t/how-do-i-connect-endress-hauser-liquiline-cm-448-controllers-with-profinet-output-to-ignition/71376/1 "2023-03-21T13:55:41Z")

</div>

We are in the process of installing multiple Endress+Hauser Liquiline CM-448 controllers with Profinet output to monitor tank solution concentration, conductivity, and temperature. Is there a driver that can be set up in Ignition to support Profinet output?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 21, 2023, 1:59pm UTC](https://forum.inductiveautomation.com/t/how-do-i-connect-endress-hauser-liquiline-cm-448-controllers-with-profinet-output-to-ignition/71376/2 "2023-03-21T13:59:29Z")

</div>

No, you'll need to see if this vendor offers an OPC server, or if another 3rd party like Kepware might have support for these controllers.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 21, 2023, 2:01pm UTC](https://forum.inductiveautomation.com/t/how-do-i-connect-endress-hauser-liquiline-cm-448-controllers-with-profinet-output-to-ignition/71376/3 "2023-03-21T14:01:14Z")

</div>

Their manual suggests it can support Modbus over RS485 if you have the right module.

> 7.3.3 Modbus  
> With the fieldbus module 485 and the appropriate device version, you can communicate  
> via Modbus RS485.  
> You use the BASE2 module for Modbus TCP.  
> The RTU and ASCII protocols are available when connecting via Modbus RS485. You can  
> switch to ASCII on the device.  
> ‣ Connect the Modbus data cable to the terminals of the fieldbus module (RS 485) or to  
> the RJ45 socket of the BASE2 module as described.  
> For detailed information on "Modbus communication", see the product pages on the  
> Internet (→ SD01189C).

---

<div class="post-metadata">

**Author:** ![Matthew\_McBride](https://avatars.discourse-cdn.com/v4/letter/m/a698b9/32.png) [@Matthew\_McBride](https://forum.inductiveautomation.com/u/Matthew_McBride)\
**Post date:** [March 21, 2023, 3:04pm UTC](https://forum.inductiveautomation.com/t/how-do-i-connect-endress-hauser-liquiline-cm-448-controllers-with-profinet-output-to-ignition/71376/4 "2023-03-21T15:04:57Z")

</div>

Thanks for the responses. Yes, E=H offer Modbus TCP or Profinet installations. We had one installed with Modbus TCP and it communicated fine with Ignition. These new controllers were purchased as part of a larger project for bulk tank storage with auto chemical additions. Based on the electrical equipment being installed to support that project it was decided to order the new controllers with Profinet output instead of Modbus TCP. We did not realize till last week that a driver for Profinet was not an option in Ignition.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 21, 2023, 3:18pm UTC](https://forum.inductiveautomation.com/t/how-do-i-connect-endress-hauser-liquiline-cm-448-controllers-with-profinet-output-to-ignition/71376/5 "2023-03-21T15:18:09Z")

</div>

Profinet support is not common in PCs. I think you need some kind of PCI-express add-in card to even get onto the network. It's much more common as a device-to-device fieldbus.

---

<div class="post-metadata">

**Author:** ![andrews](https://avatars.discourse-cdn.com/v4/letter/a/898d66/32.png) [@andrews](https://forum.inductiveautomation.com/u/andrews)\
**Post date:** [March 23, 2023, 1:49pm UTC](https://forum.inductiveautomation.com/t/how-do-i-connect-endress-hauser-liquiline-cm-448-controllers-with-profinet-output-to-ignition/71376/6 "2023-03-23T13:49:00Z")

</div>

Probably best to pass it into a PLC than Ignition