# How to Automatically Update Devices in Ignition SCADA's Devices Folder?

**URL:** <https://forum.inductiveautomation.com/t/how-to-automatically-update-devices-in-ignition-scadas-devices-folder/93658>\
**Category:** Ignition\
**Created:** [July 24, 2024, 11:47am UTC](https://forum.inductiveautomation.com/t/how-to-automatically-update-devices-in-ignition-scadas-devices-folder/93658 "2024-07-24T11:47:44Z")\
**Posts on this page:** 5\
**Page:** 1

<div class="post-metadata">

**Author:** ![Gokul\_M](https://avatars.discourse-cdn.com/v4/letter/g/e36b37/32.png) [@Gokul\_M](https://forum.inductiveautomation.com/u/Gokul_M)\
**Post date:** [July 24, 2024, 11:47am UTC](https://forum.inductiveautomation.com/t/how-to-automatically-update-devices-in-ignition-scadas-devices-folder/93658/1 "2024-07-24T11:47:44Z")

</div>

Hi Ignition Community,

I’m working with Modbus devices in Ignition SCADA and I need to automate the process of updating the Devices folder in the Designer. Specifically, I want to:

1. Automatically detect and reflect any new devices added to the Gateway in the Devices folder(took it from OPC Browser).
2. What’s the best way to ensure these new devices are automatically updated and visible in the Devices folder of the Designer without manual intervention?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [July 24, 2024, 12:20pm UTC](https://forum.inductiveautomation.com/t/how-to-automatically-update-devices-in-ignition-scadas-devices-folder/93658/2 "2024-07-24T12:20:35Z")

</div>

There is no such way. Just click the refresh icon in the OPC browser whenever you open it.

---

<div class="post-metadata">

**Author:** ![Gokul\_M](https://avatars.discourse-cdn.com/v4/letter/g/e36b37/32.png) [@Gokul\_M](https://forum.inductiveautomation.com/u/Gokul_M)\
**Post date:** [July 26, 2024, 5:05am UTC](https://forum.inductiveautomation.com/t/how-to-automatically-update-devices-in-ignition-scadas-devices-folder/93658/3 "2024-07-26T05:05:35Z")

</div>

Thank you for your reply

---

<div class="post-metadata">

**Author:** ![michael.flagler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.flagler/32/26272_2.png) [@michael.flagler](https://forum.inductiveautomation.com/u/michael.flagler)\
**Post date:** [July 26, 2024, 2:21pm UTC](https://forum.inductiveautomation.com/t/how-to-automatically-update-devices-in-ignition-scadas-devices-folder/93658/4 "2024-07-26T14:21:53Z")

</div>

Also, if you're trying to browse modbus devices, that means you're probably using the mapping feature which isnt' really the best way of going about using Modbus. In your OPC tags, it's better to direclty reference the registers using the modbus addressing format.

For example:

```python
40001 (int) = "ns=1;s=[DeviceName]HR1"
40035 (float) = "ns=1;s=[DeviceName]HRF35"

```

See: [Modbus Addressing | Ignition User Manual](https://www.docs.inductiveautomation.com/docs/8.1/ignition-modules/opc-ua/opc-ua-drivers/modbus/modbus-addressing#manually-addressing-a-modbus-device)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [July 26, 2024, 8:44pm UTC](https://forum.inductiveautomation.com/t/how-to-automatically-update-devices-in-ignition-scadas-devices-folder/93658/5 "2024-07-26T20:44:07Z")

</div>

> [@michael.flagler](#):
>
> probably using the mapping feature

Well, they **could** be using my alternate driver, which **does** show possible addresses in the OPC browser...