You haven't mentioned PLC type, but your screen shot suggests Rockwell.

If so you may be able to leverage the [Diagnostics]Device/Status tag.

> [@Logix Device Status](http://forum.inductiveautomation.com/t/logix-device-status/24103/4):
>
> The CIP Spec has some generic definitions for the bits in that word in Volume 3, table 5A-2.3 and table 5A-2.4, and requires that the reserved/vendor bits there, if used, be declared in the device’s EDS file. Bit 0: "Owned". Not applicable to a processor, I would think. Bit 1: Reserved. Bit 2: "Configured". Probably always true except when at factory default. Bit 3: Reserved. Bits 4-7: 4-bit integer extended status code: 0: Self test/unknown 1: Firmware updating 2: Any Faulted I/O co…

---

_[View the full topic](https://forum.inductiveautomation.com/t/how-to-detect-plc-failure/25631)._